Old 06-20-2024, 10:25 AM   #41
Senior Member
 
Join Date: Mar 2019
Location: Nevada
Posts: 1,981
It is amazing to me that the idea of using a 240 volt power source keeps coming up when it comes to powering travel trailers.
ppine is offline  
Old 06-20-2024, 10:28 AM   #42
Senior Member
 
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 10,300
Aha!

Quote:
Originally Posted by ppine View Post
It is amazing to me that the idea of using a 240 volt power source keeps coming up when it comes to powering travel trailers.
Aha! Never underestimate the ignorance of the American people.
__________________
Larry
"Everybody's RV is not like your RV."
"Always take pictures with the button on the right."
"Always bypass the water heater before opening the low-point drains."
Sticks and Bricks: Raleigh, NC
2008 Cherokee 38P: at Ivor, VA permanently
Larry-NC is offline  
Old 06-20-2024, 10:30 AM   #43
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 34,930
Quote:
Originally Posted by ppine View Post
It is amazing to me that the idea of using a 240 volt power source keeps coming up when it comes to powering travel trailers.
Not really understanding this comment as ALL 50 amp travel trailers use a 120/240 volt split phase service.

https://www.rvtechmag.com/electrical/chapter3.php
__________________
2011 Flagstaff 831 RLBSS

Sometimes I wonder why I'm not in an asylum. Then I take a good look around at everyone and realize...Maybe I am.
wmtire is online now  
Old 06-20-2024, 11:03 AM   #44
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,511
Quote:
Originally Posted by ppine View Post
It is amazing to me that the idea of using a 240 volt power source keeps coming up when it comes to powering travel trailers.
Why?
All 50a R/Vs utilize a 240v supply to the R/V.
It is the R/V's power distribution center (breaker box) that keeps the two phases separate and everything operating on 120v.
Not amazing at all.
Attached Thumbnails
Click image for larger version

Name:	50 amp rv service_01.JPG
Views:	12
Size:	35.3 KB
ID:	301156   Click image for larger version

Name:	50 amp rv service_02.JPG
Views:	12
Size:	46.8 KB
ID:	301157  
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=101
5picker is offline  
Old 06-20-2024, 12:31 PM   #45
Senior Member
 
Join Date: Apr 2022
Location: Tarpon Springs FL
Posts: 4,789
Aussieland and I think europe use 240v on a single line

awww now I am really confused
__________________
Tarpon Springs FL
2022 Salem 24RLXL
Aussieguy is offline  
Old 06-20-2024, 01:13 PM   #46
Senior Member
 
Join Date: Apr 2021
Posts: 2,904
Quote:
Originally Posted by Aussieguy View Post
Aussieland and I think europe use 240v on a single line

awww now I am really confused
Yep, 230V at 50 Hz is the standard for EU and AU. They drive on the wrong side of the road too.

Bob
Bob K4TAX is offline  
Old 06-20-2024, 02:07 PM   #47
Senior Member
 
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 10,300
History...

Quote:
Originally Posted by Aussieguy View Post
Aussieland and I think europe use 240v on a single line

awww now I am really confused
History. Electric distribution (and telephony) developed independently in different countries. By the time globalization occurred (when everyone wanted to sell their products in other countries), the local standards were in wide use and no one could practically change. Different voltages, frequencies, and plug/outlet types all over.

The technologies that achieved universal usage were developed after globalization: Ethernet, Wi-Fi 802.11b/g/n/ac/ac, GSM, SMS, 3G/4G/5G, USB 1/2/3, all the modem standards after 300 bps, etc.
__________________
Larry
"Everybody's RV is not like your RV."
"Always take pictures with the button on the right."
"Always bypass the water heater before opening the low-point drains."
Sticks and Bricks: Raleigh, NC
2008 Cherokee 38P: at Ivor, VA permanently
Larry-NC is offline  
Old 06-21-2024, 10:29 AM   #48
Senior Member
 
Join Date: Mar 2019
Location: Nevada
Posts: 1,981
5picker has eloquently hinted at why people are so confused.
30 amp service one hot leg, neutral and a ground.
50 amp service, 2 hot legs, neutral and a ground.
But RVs do not use 240 volt equipment.

Do some RVs have 240 volt circuits for ovens and dryers?"
ppine is offline  
Old 06-21-2024, 10:32 AM   #49
Senior Member
 
Join Date: Apr 2022
Location: Tarpon Springs FL
Posts: 4,789
on a 50 amp each leg can supply 50amps
= 100amps usable


I ve still got a headache
__________________
Tarpon Springs FL
2022 Salem 24RLXL
Aussieguy is offline  
Old 06-21-2024, 10:53 AM   #50
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 34,930
Quote:
Originally Posted by ppine View Post

Do some RVs have 240 volt circuits for ovens and dryers?"
Yes, here a few examples from Camping World

https://www.campingworld.com/furrion...E&gclsrc=aw.ds

https://www.campingworld.com/equator...E&gclsrc=aw.ds
__________________
2011 Flagstaff 831 RLBSS

Sometimes I wonder why I'm not in an asylum. Then I take a good look around at everyone and realize...Maybe I am.
wmtire is online now  
Old 06-21-2024, 11:07 AM   #51
Senior Member
 
Join Date: Apr 2021
Posts: 2,904
Quote:
Originally Posted by Aussieguy View Post
on a 50 amp each leg can supply 50amps
= 100amps usable


I ve still got a headache

L1 is electrically 180-degree phase voltage difference than L2. Likewise, the current in each leg is also 180-degree phase difference. For each 50 amp leg to be used to obtain 100 amps, the voltage has to be added.

However, with a 50 amp service, a total of 12,000 watts is available, but not at 100 amps. Only 50 amps per leg maximum.

Bob
Bob K4TAX is offline  
Old 06-21-2024, 01:44 PM   #52
Member
 
Join Date: Sep 2023
Posts: 58
Can't over emphasize using a good cord. 10ga and as short as possible.

I was reminded this recently as just charging my batteries on a 100' 14ga cord would drive the voltage below the transfer switch cutoff and throw the breaker. Just too much voltage drop between the 15a plug and the RV
thudd3r is offline  
Old 06-21-2024, 02:46 PM   #53
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,511
Quote:
Originally Posted by Bob K4TAX View Post
L1 is electrically 180-degree phase voltage difference than L2. Likewise, the current in each leg is also 180-degree phase difference. For each 50 amp leg to be used to obtain 100 amps, the voltage has to be added.

However, with a 50 amp service, a total of 12,000 watts is available, but not at 100 amps. Only 50 amps per leg maximum.

Bob
Bob is exactly right.
Many folks think they are getting 12,000w/100a of power available throughout but in reality it is 6,000w/50a of power on each leg for a COMBINED TOTAL of 12,000/100a. Anything more than 50a on either leg, trips the mechanically connected double breaker.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=101
5picker is offline  
Old 06-22-2024, 03:28 PM   #54
Senior Member
 
Join Date: Mar 2019
Location: Nevada
Posts: 1,981
Use a 20 amp circuit , 12 gauge wiring. Use an extension cord that is at least 12 ga, 10 ga is much better.
ppine is offline  
Old 06-24-2024, 06:24 PM   #55
Senior Member
 
Join Date: Nov 2020
Posts: 543
Absolutely do not use the dryer outlet

Quote:
Originally Posted by Twinboat View Post
Although everybody says you can't go with option #2, if your sons dryer has a NEMA 14-30 R receptacle ( 4 conductor ), you can.
Pickup this adaptor and you can access your full 30 amp service.
ABSOLUTELY DO NOT USE THE DRYER OUTLET IT S 240V. 110v/220v hasn't existed for A very long time. Everything is now 120v/240v. Your camper is now 120v only! Your sons dryer will NOT HAVE A NEMA 14-30r outlet unless someone wired the wrong outlet. Electric Dryers never use 120v. If you use that outlet you WILL FRY YOUR TRAILER ELECTRICAL.


Most electric dryers are rated at 240 volt. The nominal voltage is 240 volt, but homes may have 208V, 220V, or 240V power supply. Any appliance that is rated for 240 volts can also be used on a 220V or 208V outlet.

You could add a soft starter and probably use a 12 ga cord safely. Not 14 or 16 ga.
dedobias is offline  
Old 06-24-2024, 06:45 PM   #56
Junior Member
 
Join Date: Dec 2023
Posts: 13
Just a quick reply with my experience. Yes, I have plugged my 30a, 25fkbs into my garage outlet. The AC worked fine. I did not try to run any other high amp items at the same time.
andyalex is offline  
Old 06-24-2024, 06:46 PM   #57
Senior Member
 
gw1800's Avatar
 
Join Date: Aug 2016
Posts: 562
Quote:
Originally Posted by Chuck_S View Post
My Roo AC will run off the 120vAC outlet in my garage so yours probably will too but I don't try to run the electric water heater or microwave at the same time.

-- Chuck
Or a coffee pot, or electric space heater.
__________________
Western PA
2015 Silverado Z71
2018 toy hauler
gw1800 is offline  
Old 06-24-2024, 06:47 PM   #58
Senior Member
 
Join Date: Nov 2020
Posts: 543
Quote:
Originally Posted by andyalex View Post
Just a quick reply with my experience. Yes, I have plugged my 30a, 25fkbs into my garage outlet. The AC worked fine. I did not try to run any other high amp items at the same time.
To be clear, a 120v outlet.
dedobias is offline  
Old 06-24-2024, 06:48 PM   #59
Senior Member
 
Join Date: Nov 2020
Posts: 543
The standard voltage in the United States and Canada was changed from 110 volts to 120 volts about 75 years ago, depending on the region. The national standard specifies that the nominal voltage at the source should be 120 volts, with a range of 114–126 volts (RMS).
dedobias is offline  
Old 06-24-2024, 07:35 PM   #60
AWF 1957
 
dshome's Avatar
 
Join Date: Aug 2014
Location: Houston area
Posts: 25
Quote:
Originally Posted by Outsider View Post
We're going to my son's in GA in 2 weeks and will be parking our Geo Pro G19FD beside his house to live out of for 3-4 days. The air conditioner in the camper is on a 15 amp breaker so I'm wondering if plugging into a common 15A outside outlet at his house will be supply sufficient current to run it properly. (I remember once last year we had to run the air through a 25 foot 12/2 extension cord to the 15A outlet on a campsite post and the outlet there got somewhat hot.) We will primarily be using the camper to sleep in, may even be showering in his house.


Or, option 2, is there a way I can plug my camper 220 VAC cord into his dryer outlet in his basement and run off of it?


Thanks for your insight.


Outsider.
https://www.microair.net/collections...-soft-starters

Install one of those and you can power most everything.
__________________
AWF #1957
dshome is offline  
Closed Thread

Tags
air conditioner

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 06:33 PM.