Furnace will not shut off.

A couple of nights ago. We had our thermostat set to 72. Woke up hot, checked the thermostat, temp was 85. thermostat was still set to 72. Furnace was running, and would not shut off. So, I turned off the propane. Furnace of course went off then. Now its cold again, and the heat strips in the overheads, and the fireplace just aren't cutting it. Tried firing up the furnace again. Nothin! Any ideas? It is a Rockwood Signature 2017. Any help would be appreciated. I have a short manual for the furnace, doesn't give any troubleshooting in it. Just a wiring diagram.
Huntxtrm1 is offline   Reply With Quote
Old 03-03-2019, 01:51 PM   #2
Senior Member
 
Join Date: Jun 2012
Posts: 10,907
Assuming it's a Suburban, I've attached a service manual. Might help if you posted what make/model of thermostat you have.
Attached Files
File Type: pdf Suburban Furnace Service Manual.pdf (4.92 MB, 77 views)
__________________
1988 Coleman Sequoia - popup (1987-2009) - outlasted 3 Dodge Grand Caravans!
2012 Roo19 - hybrid (2012-2015)

2016 Mini Lite 2503S - tt (2015 - ???)
2011 Traverse LT, 3.6L, FWD
2009 Silverado 1500 Ext Cab, 5.3L, 4x4, 3.73
2016 Silverado 2500HD Dbl Cab, 6.0L 4x4, 4.10
rockfordroo is offline   Reply With Quote
Old 03-03-2019, 02:11 PM   #3
Senior Member
 
Join Date: Mar 2014
Location: Mountain Foothills of Southern Alberta
Posts: 1,334
You may need to purge the propane line to the furnace. Keep trying to run the furnace and this will eventually purge the line.
Is the fan coming on when you try running the furnace?
__________________

2007 Surveyor SV230
- 200 Watts Solar/MPPT Controller - 230 AH Battery Bank - 600 watt PSW Inverter - (2) 2000 watt Inverter Generators - LED Lighting
2009 F150 - 5.4 Litre - Tow Package
Boon Docking 99% of the time.
boondocking is offline   Reply With Quote
Old 03-03-2019, 02:34 PM   #4
Site Team
 
Flybob's Avatar
 
Join Date: Oct 2014
Posts: 11,861
If the thermostat was still calling for heat ( defective) and you shut off the propane, the furnace tried to light several times but did not as there was no propane. This caused the safety to kick in and it is in safe mode. You need to disconnect 12V power from the control by pulling the fuse for the furnace. Wait a few minutes then reinsert the fuse. With propane on it should fire up fine. As for the thermostat, if it is a digital one you should reset it.
If you have a Dometic 4 or 5 button thermostat.

Reset the thermostat to factory specs. This can correct some problems with invalid temperature measurement when the thermistor inside the thermostat is being used. This sequence definitely works with 4-button thermostats. I do not have a 5-button unit to test so I cannot say if it works on 5-button thermostats. Do the following in the order below:
-- Turn the thermostat on
-- press any button once
-- press and hold the bottom 2 buttons in
-- press and release the mode button one time
-- release the bottom 2 buttons
-- press and release the mode button
-- if you did the above sequence correctly, the thermostat backlight will turn off. If it does not turn off, do the above sequence again.
__________________

2015 Freedom Express 248RBS
TV 2015 Silverado HD2500 Duramax
TST Tire Monitors
Honda 2000I + Companion
2 100W solar panels
Flybob is online now   Reply With Quote
Old 03-03-2019, 02:54 PM   #5
Site Team
 
KyDan's Avatar
 
Join Date: Mar 2008
Location: Louisville, KY
Posts: 9,128
What he said except you can pull the furnace fuse and count to 10 and plug it back in.
That should reset the fault that was generated when you shut off the propane.
Next time you need to kill the furnace you can just pull the fuse.
__________________
Peace!
Dan & Rita D
2017 Nissan Titan 5.6L King cab 4wd
1999 Suzuki Intruder Motorcycle
Blue Ox WD hitch

Camping days 2010-53, 2011-47, 2012-41, 2013-41, 2014-31, 2015-40, 2016-44, 2017-63, 2018-75, 2019-32, 2020-41
KyDan is online now   Reply With Quote
Old 03-03-2019, 04:03 PM   #6
Usually Confused Member
 
emm-dee's Avatar
 
Join Date: Nov 2015
Location: Georgia
Posts: 3,468
Quote:
Originally Posted by KyDan View Post
What he said except you can pull the furnace fuse and count to 10 and plug it back in.
That should reset the fault that was generated when you shut off the propane.
Next time you need to kill the furnace you can just pull the fuse.
No, donít pull the fuse while the furnace is running. If you turn it OFF at the thermostat control box the fire will stop but the fan will continue to run until the furnace cools down. Pulling the fuse will stop the propane flow and the cooling fan. That defeats one of the main safety features built in.

If selecting OFF on the thermostat doesnít work then the thermostat is defective and should be replaced.
__________________
2018 Forester 3051S (aka Clyde)
2015 Wrangler Toad (aka Bonnie)

At some point during every day you suddenly realize nothing else productive is going to happen the rest of that day. For me, it usually occurs around 9 am.
emm-dee is online now   Reply With Quote
Old 03-04-2019, 09:32 AM   #7
Site Team
 
KyDan's Avatar
 
Join Date: Mar 2008
Location: Louisville, KY
Posts: 9,128
Pulling the furnace fuse will not allow the furnace to run the short cool down but it will shut down the burner and fan.
I see no harm in doing that once or twice while trying to trouble shoot a problem.
__________________
Peace!
Dan & Rita D
2017 Nissan Titan 5.6L King cab 4wd
1999 Suzuki Intruder Motorcycle
Blue Ox WD hitch

Camping days 2010-53, 2011-47, 2012-41, 2013-41, 2014-31, 2015-40, 2016-44, 2017-63, 2018-75, 2019-32, 2020-41
KyDan is online now   Reply With Quote
Old 03-04-2019, 09:49 AM   #8
Site Team
 
Flybob's Avatar
 
Join Date: Oct 2014
Posts: 11,861
OP said the furnace would not shut off via the thermostat so he had to turn off propane to force it to shut off. This forced the furnace into safe mode so it will not restart until it is reset.
__________________

2015 Freedom Express 248RBS
TV 2015 Silverado HD2500 Duramax
TST Tire Monitors
Honda 2000I + Companion
2 100W solar panels
Flybob is online now   Reply With Quote
Old 03-05-2019, 11:27 AM   #9
Commercial Member
 
ES_FR's Avatar
 
Join Date: May 2018
Posts: 337
Huntxtrm1,

Thank you for being a part of the Rockwood family.

Please accept our sincerest apologies for any inconveniences that you have experienced with your new Rockwood Signature Ultra Lite. Your satisfaction is very important to us; accordingly, we invite you to contact Rayna Dimitroff in our Customer service department through the following personalized and direct link: Forest River RV Direct Service Contact - Forest River, Inc..

This direct link is provided for your convenience in order that we may resolve your concerns as quickly as possible. We will strive to respond to you within 24 hours of receiving your correspondence.

Respectfully,
Forest River
ES_FR is offline   Reply With Quote
Reply

Tags
furnace

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 06:25 PM.