Stumper Atwood 2540 problem

I am having a really annoying problem with my older atwood 2540 2 stage furnace (8900-III). It is an older furnace so parts have become limited.

Every time the furnace shuts down, we get a propane odour. Sometimes weak, sometimes very strong. It also has melted 2 combustion wheels. There are also signs of incomplete combustion (lots of soot, etc) I have blown and sucked out the combustion chamber to clear any obstructions. Burner head also looks fine.

I can hear that propane valves are delayed in closing some of the time... I know it is supposed shut off the propane, and then the blower keep running to evacuate the exhaust, but it seems like the valves are being told to stay open until the fan shuts off and then they close afterwards - I have confirmed this by putting a multimeter on the solenoid valve connection and there is power to it until after the fan shuts off and then the valves lose power and you can hear them click shut.... so it doesn't seem like a mechanical jamming/failure in the solenoid valves itself. It seems to me like they should close immediately and then the fan should run for another 30 seconds (or whatever the time delay is) When you turn it off at the thermostat the fan runs for a while still so the fan is still on a time delay of some sort.

This leads me to conclude that the valves are being told to stay open by the logic board(s) until after the fan shuts off, which seems like the incorrect sequence of events? The odd time I can hear a poof after it shuts down as well... This make me think that it has propane in the combustion chamber and when the fan shuts down it is depleted of oxygen to the point that the flame is nearly extinguished and the odd time there is a small explosion due to the excess propane stuck in there.... which is causing the soot and melting the combustion wheel... also the propane smell.

I have tried replacing the ignition board... It didn't make any difference. I know it seems like a strange way for a logic board to fail but I'm not sure what else to conclude if it is being told to stay open. There are two boards in my unit, the "dual control" board and the "ignition board"... do you think it's worth changing the dual control board? I started with the ignition board because it is the one that the wires run to the propane valves.... but the control boards are tied together with a couple wires so perhaps this logic portion comes from the other board, and the ignition board is simply a relay for power to go to the solenoid valves.

The propane smell goes away completely after it has shut down for a while and airs out.

Anyone ever see or hear of this happening before?
any ideas?

thanks,
coastRVer is offline   Reply With Quote
Old 12-10-2021, 12:03 AM   #2
Senior Member
 
Join Date: Feb 2018
Location: TEXAS
Posts: 9,208
Quote:
Originally Posted by coastRVer View Post
when the fan shuts down it is depleted of oxygen to the point that the flame is nearly extinguished and the odd time there is a small explosion due to the excess propane stuck in there.... which is causing the soot and melting the combustion wheel... also the propane smell.
A small explosion! Unfortunately, I can't help you solve the problem, but you need to find someone who can or replace that furnace.
__________________
2015 Dynamax REV 24TB class C
Reverse_snowbird is offline   Reply With Quote
Old 12-10-2021, 10:07 AM   #3
Senior Member
 
SeaDog's Avatar
 
Join Date: Jan 2016
Location: x
Posts: 12,423
Welcome to the forum its a great place to get your questions answered. What rig do you have Make, Model, year. Sounds to me like a faulty gas valve. JMHO
__________________
Retired Navy
Jake my sidekick (yellow Lab) 10/04 - 05/20
2017 RAM 2500 CC 4X4 Cummins Diesel
2016 Flagstaff 26 FKWS
AF&AM & El Korah Shrine of Idaho
SeaDog is offline   Reply With Quote
Old 12-10-2021, 01:52 PM   #4
Senior Member
 
Join Date: Mar 2014
Location: Mountain Foothills of Southern Alberta
Posts: 2,004
Quote:
Originally Posted by SeaDog View Post
Welcome to the forum its a great place to get your questions answered. What rig do you have Make, Model, year. Sounds to me like a faulty gas valve. JMHO
Atwood 2540
__________________

2007 Surveyor SV230
- 200 Watts Solar/MPPT Controller - 220 AH Battery Bank (Two-GC2) - 600 watt PSW Inverter - (2) 2000 watt Inverter Generators - LED Lighting
2009 F150 - 5.4 Litre with Tow Package

Boon Docking 99% of the time.
boondocking is offline   Reply With Quote
Old 12-10-2021, 01:58 PM   #5
Site Team
 
bikendan's Avatar
 
Join Date: Jan 2007
Location: Goodyear, Arizona
Posts: 33,790
Quote:
Originally Posted by boondocking View Post
Atwood 2540
I think he was asking for information on the OP's RV, not the furnace.
__________________
Dan-Retired California Firefighter/EMT
Shawn-Musician/Entrepreneur/Wine Expert
and Zoe the Wonder Dog(R.I.P.)
2016 PrimeTime TracerAIR 255, pushing a 2014 Ford F150 SCREW XTR 4x4 3.5 Ecoboost w/Max Tow Package
4pt Equal-i-zer WDH and 1828lbs of payload capacity
bikendan is offline   Reply With Quote
Old 12-10-2021, 02:40 PM   #6
Senior Member
 
Join Date: Mar 2014
Location: Mountain Foothills of Southern Alberta
Posts: 2,004
Quote:
Originally Posted by bikendan View Post
I think he was asking for information on the OP's RV, not the furnace.
Are different models of the Atwood 2540 put into different models of Trailers?
__________________

2007 Surveyor SV230
- 200 Watts Solar/MPPT Controller - 220 AH Battery Bank (Two-GC2) - 600 watt PSW Inverter - (2) 2000 watt Inverter Generators - LED Lighting
2009 F150 - 5.4 Litre with Tow Package

Boon Docking 99% of the time.
boondocking is offline   Reply With Quote
Old 12-10-2021, 02:50 PM   #7
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,143
Quote:
Originally Posted by boondocking View Post
Are different models of the Atwood 2540 put into different models of Trailers?
I'm not jumping into the middle of this particular query but... some folks believe so.

I had a fellow a few weeks ago tell me on another R/V forum that the Suburban SW10DEL water heater in his Jayco Pinnacle Luxury 5th wheel was NOT the same model they put in less expensive makes/models.

Back to your regularly scheduled programming...
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=90
5picker is online now   Reply With Quote
Old 12-10-2021, 03:12 PM   #8
Senior Member
 
SeaDog's Avatar
 
Join Date: Jan 2016
Location: x
Posts: 12,423
The reason for asking was to so that someone on the forum with the same rig who may not know the furnace model might be able to provide an answer. I fully understand a model of furnace regardless of what it is installed in is the same furnace I didn't just fall of the turnip truck on the way to town.
__________________
Retired Navy
Jake my sidekick (yellow Lab) 10/04 - 05/20
2017 RAM 2500 CC 4X4 Cummins Diesel
2016 Flagstaff 26 FKWS
AF&AM & El Korah Shrine of Idaho
SeaDog is offline   Reply With Quote
Old 12-10-2021, 03:19 PM   #9
Site Team
 
Mr. Dan's Avatar
 
Join Date: Mar 2014
Location: Grayson County, Texas
Posts: 21,560
Quote:
Originally Posted by SeaDog View Post
The reason for asking was to so that someone on the forum with the same rig who may not know the furnace model might be able to provide an answer. I fully understand a model of furnace regardless of what it is installed in is the same furnace I didn't just fall of the turnip truck on the way to town.
Speaking of "turnip truck", this one was mine!
Attached Thumbnails
Click image for larger version

Name:	Turnip Ground Cleared.jpg
Views:	47
Size:	215.6 KB
ID:	266591  
__________________
2015 FR Wildcat 295RSX / GMC Sierra

Nights Camped: '13 = 49/'14 = 74/'15 = 74/'16 = 85/'17 = 110/'18 = 111/'19 = 86/'20 =108/'21 = 115/'22 = 135/'23 = 78; Booked for 2024 = 69
Mr. Dan is online now   Reply With Quote
Old 12-10-2021, 03:27 PM   #10
Senior Member
 
Join Date: Mar 2014
Location: Mountain Foothills of Southern Alberta
Posts: 2,004
LOL
__________________

2007 Surveyor SV230
- 200 Watts Solar/MPPT Controller - 220 AH Battery Bank (Two-GC2) - 600 watt PSW Inverter - (2) 2000 watt Inverter Generators - LED Lighting
2009 F150 - 5.4 Litre with Tow Package

Boon Docking 99% of the time.
boondocking is offline   Reply With Quote
Old 12-10-2021, 03:32 PM   #11
Senior Member
 
SeaDog's Avatar
 
Join Date: Jan 2016
Location: x
Posts: 12,423
its an old time saying, good pic LOL
__________________
Retired Navy
Jake my sidekick (yellow Lab) 10/04 - 05/20
2017 RAM 2500 CC 4X4 Cummins Diesel
2016 Flagstaff 26 FKWS
AF&AM & El Korah Shrine of Idaho
SeaDog is offline   Reply With Quote
Old 12-10-2021, 03:35 PM   #12
Senior Member
 
Join Date: Mar 2014
Location: Mountain Foothills of Southern Alberta
Posts: 2,004
Quote:
Originally Posted by coastRVer View Post

I have tried replacing the ignition board... It didn't make any difference. I know it seems like a strange way for a logic board to fail but I'm not sure what else to conclude if it is being told to stay open. There are two boards in my unit, the "dual control" board and the "ignition board"... do you think it's worth changing the dual control board? I started with the ignition board because it is the one that the wires run to the propane valves.... but the control boards are tied together with a couple wires so perhaps this logic portion comes from the other board, and the ignition board is simply a relay for power to go to the solenoid valves.

The propane smell goes away completely after it has shut down for a while and airs out.



thanks,
Is there any way to interrupt the connection between the two boards while this problem is happening. To see if the gas valve powers down.
__________________

2007 Surveyor SV230
- 200 Watts Solar/MPPT Controller - 220 AH Battery Bank (Two-GC2) - 600 watt PSW Inverter - (2) 2000 watt Inverter Generators - LED Lighting
2009 F150 - 5.4 Litre with Tow Package

Boon Docking 99% of the time.
boondocking is offline   Reply With Quote
Old 12-12-2021, 11:35 AM   #13
Senior Member
 
Join Date: Apr 2019
Posts: 648
Quote:
Originally Posted by coastRVer View Post
I am having a really annoying problem with my older atwood 2540 2 stage furnace (8900-III). It is an older furnace so parts have become limited.

Every time the furnace shuts down, we get a propane odour. Sometimes weak, sometimes very strong. It also has melted 2 combustion wheels. There are also signs of incomplete combustion (lots of soot, etc) I have blown and sucked out the combustion chamber to clear any obstructions. Burner head also looks fine.

I can hear that propane valves are delayed in closing some of the time... I know it is supposed shut off the propane, and then the blower keep running to evacuate the exhaust, but it seems like the valves are being told to stay open until the fan shuts off and then they close afterwards - I have confirmed this by putting a multimeter on the solenoid valve connection and there is power to it until after the fan shuts off and then the valves lose power and you can hear them click shut.... so it doesn't seem like a mechanical jamming/failure in the solenoid valves itself. It seems to me like they should close immediately and then the fan should run for another 30 seconds (or whatever the time delay is) When you turn it off at the thermostat the fan runs for a while still so the fan is still on a time delay of some sort.

This leads me to conclude that the valves are being told to stay open by the logic board(s) until after the fan shuts off, which seems like the incorrect sequence of events? The odd time I can hear a poof after it shuts down as well... This make me think that it has propane in the combustion chamber and when the fan shuts down it is depleted of oxygen to the point that the flame is nearly extinguished and the odd time there is a small explosion due to the excess propane stuck in there.... which is causing the soot and melting the combustion wheel... also the propane smell.

I have tried replacing the ignition board... It didn't make any difference. I know it seems like a strange way for a logic board to fail but I'm not sure what else to conclude if it is being told to stay open. There are two boards in my unit, the "dual control" board and the "ignition board"... do you think it's worth changing the dual control board? I started with the ignition board because it is the one that the wires run to the propane valves.... but the control boards are tied together with a couple wires so perhaps this logic portion comes from the other board, and the ignition board is simply a relay for power to go to the solenoid valves.

The propane smell goes away completely after it has shut down for a while and airs out.

Anyone ever see or hear of this happening before?
any ideas?

thanks,

You are talking about GAS AND FIRE!
GET A PROFESSIONAL BEFORE SOMETHING BAD HAPPENS!
__________________
.
campers302 is offline   Reply With Quote
Old 12-12-2021, 12:20 PM   #14
Senior Member
 
Join Date: May 2017
Posts: 5,712
Question: How do the burners go out if the valves are not closing right away ??
TheWolfPaq82 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 08:05 AM.