Help! We are plugged into 30 amp shore power at a campground. We accidently over loaded the circuit running electric heater, convection oven, hair dryer. We restart the GFI in panel by bed, and reset the magnum invertor outside. Still have a red fault light and blinking chg light on magnum panel with dead battery charge dc 0.4v. We have no 110 outlets. What are we missing,? Husband has discovered that half of the split bus in the circuit panel by the bed has no power. ISATA 5
|
Hind sight eval:
1. overloaded 30amp 120 connection >3600 watts power
2. reset breakers and have magnum inverter fault no charge to batteries.
3. half of electrical buss --- no power
As a reminder, the inverter is pass thru for the 120 power. The charging circuits internally are on only one leg of the incoming power.
When the 30 amp feed dropped offlne due to overcurrent draw, the inverter tried to take over using battery power. The level of draw that was occurring was >3600 watts. Power to support that from 12v source would be >300amp.
12v fuse to inverter would definitely "pop" especially if it is a 200 amp fuse.
So, anytime anyone experiences an overload, one needs to not only restore AC input power but verify that the DC side to the inverter is still good.
Keep this in mind folks!