Old 12-01-2021, 05:27 PM   #1
Senior Member
 
twp5253's Avatar
 
Join Date: May 2018
Posts: 444
Which NEMA 14-50 R and P connectors to use?

I like the idea of wiring connectors in my elec bay so I can put the Hughes PWD50-EPO into the locked bay. Also, if it were to fail, be able to bypass it.
Brilliant Magnatudes! Now, when the coach I ordered arrives in 22 I will be wondering what connectors I should use. I see lots of NEMA 14-50P and Rs out there but I have also seen pictures of some of them melted. I found a Hubbell 14-50P that looks real beefy but they don't make a similar 14-50R other than a surface mount unit. So, what connectors should I use and can I be confident they will handle the full 50amp Monty? Thank you very much, Thorne
__________________
2022 DynaQuest XL 3400KD CabOver, WD, Lithium Batteries, 4 190Watt Rigid Panels, extra inverter for AC operation w/o Genset.
twp5253 is offline   Reply With Quote
Old 12-01-2021, 07:08 PM   #2
Senior Member
 
Join Date: Nov 2019
Posts: 1,424
Quote:
Originally Posted by twp5253 View Post
I like the idea of wiring connectors in my elec bay so I can put the Hughes PWD50-EPO into the locked bay. Also, if it were to fail, be able to bypass it.
Brilliant Magnatudes! Now, when the coach I ordered arrives in 22 I will be wondering what connectors I should use. I see lots of NEMA 14-50P and Rs out there but I have also seen pictures of some of them melted. I found a Hubbell 14-50P that looks real beefy but they don't make a similar 14-50R other than a surface mount unit. So, what connectors should I use and can I be confident they will handle the full 50amp Monty? Thank you very much, Thorne
Can't go wrong with a Hubbell or Levington brand. If you've seen any melted it because a wire connection was loose either inside the connector body or the plug and receptacle mating surfaces didn't fit tight
__________________
2019 F150 4X4 7050 GVWR 1903 payload
2018 Avenger 21RBS 7700 GVWR
Mike134 is offline   Reply With Quote
Old 12-01-2021, 07:40 PM   #3
D W
Senior Member
 
D W's Avatar
 
Join Date: Sep 2016
Location: ALASKA (World's Biggest Campground)
Posts: 6,705
You should be using 6/3 wire with ground. Any UL approved 14-50P or R will suffice. They are capable of carrying 50 amps on both legs for a total of 100 amps. The reason you see some melted is due to loose or poor connections either in the plug or receptacle. A flush mount is designed to be installed in an appropriate gang box with suitable wall plate.
__________________
'07 K3500 Silverado LT Crew Duramax (LBZ)
2016 Salem 27RKSS
1984 CHEV SCOTTSDALE K20 2GCGK24J0E1XXXXXX (Chevrolet Legends-Class of 2019)
"...exhaust fluid? We don't need no stinkin' exhaust fluid"
D W is offline   Reply With Quote
Old 12-01-2021, 11:39 PM   #4
Senior Member
 
Join Date: Jul 2020
Posts: 159
Hughes sells this kit:

https://hughesautoformers.com/produc...ll-kit-50-amp/
__________________
2021 Dynaquest 3801TS
2023 Rubicon JLU Xtreme Recon
2020 Jeep Wrangler Limited Willys
MAC D is offline   Reply With Quote
Old 12-02-2021, 12:51 AM   #5
Senior Member
 
twp5253's Avatar
 
Join Date: May 2018
Posts: 444
Quote:
Originally Posted by MAC D View Post
Purchased! Thank you. Seems really beefy, just the ticket!
__________________
2022 DynaQuest XL 3400KD CabOver, WD, Lithium Batteries, 4 190Watt Rigid Panels, extra inverter for AC operation w/o Genset.
twp5253 is offline   Reply With Quote
Old 12-02-2021, 10:09 AM   #6
D W
Senior Member
 
D W's Avatar
 
Join Date: Sep 2016
Location: ALASKA (World's Biggest Campground)
Posts: 6,705
Quote:
Originally Posted by MAC D View Post
At $108, Hughes is pretty proud of that item. The same things, 50 amp pigtail, gang box, receptacle and faceplate can be purchased at Home Depot for $50.
__________________
'07 K3500 Silverado LT Crew Duramax (LBZ)
2016 Salem 27RKSS
1984 CHEV SCOTTSDALE K20 2GCGK24J0E1XXXXXX (Chevrolet Legends-Class of 2019)
"...exhaust fluid? We don't need no stinkin' exhaust fluid"
D W is offline   Reply With Quote
Old 12-02-2021, 09:56 PM   #7
Senior Member
 
CyberShanks's Avatar
 
Join Date: May 2014
Location: Top of a hill (in Iowa) surrounded by corn.
Posts: 681
Question, I have the new hard-wired 50A Watchdog with EPO. I see that 6/3 wire is stated above with ground. What are people's thoughts on 6/2+8/1 with ground? Obviously the hots would be on 6 ga, neutral and ground on 8 ga. I see many heavy duty 50A dryer cords with this spec. What are thoughts?


Jim
__________________
2021 Dynamax Dynaquest XL 3400KD
2022 Aluma 8220H Tilt flatbed to carry:
2012 Jeep JKU Rubicon or slightly modded 2001 Jeep TJ
CyberShanks is offline   Reply With Quote
Old 12-03-2021, 12:38 AM   #8
Senior Member
 
twp5253's Avatar
 
Join Date: May 2018
Posts: 444
Quote:
Originally Posted by CyberShanks View Post
Question, I have the new hard-wired 50A Watchdog with EPO. I see that 6/3 wire is stated above with ground. What are people's thoughts on 6/2+8/1 with ground? Obviously the hots would be on 6 ga, neutral and ground on 8 ga. I see many heavy duty 50A dryer cords with this spec. What are thoughts?


Jim
Not an electrician but I often play one with homes, cars, boats and motorcycles. The Hots and the common need to be the same size. The reason one common works with two hots in a 240volt scenario is that the current is exactly out of phase so the common only ever sees what one of the hots has at a time and then cycles to what the other hot sees. That may not make sense but you need the hot and the common to be the same size. Its only the ground that can be smaller because it really only acts as an emergency relief.

Can you please post up some pictures of the area your working on as I am trying to get parts to wire in the removable Watchdog. My thinking is that I want it in the locked bay but I also want the option to remove it from the circuit should it take a dump/lightning strike
__________________
2022 DynaQuest XL 3400KD CabOver, WD, Lithium Batteries, 4 190Watt Rigid Panels, extra inverter for AC operation w/o Genset.
twp5253 is offline   Reply With Quote
Old 12-03-2021, 10:19 AM   #9
Senior Member
 
CyberShanks's Avatar
 
Join Date: May 2014
Location: Top of a hill (in Iowa) surrounded by corn.
Posts: 681
I have a new jumper wire on order, I'm currently only connected to 30A.


The coach power feed is the one on the right, it's an armored cable, has 6/3 with probably an 18 or smaller gauge ground. The one on the left is the dryer cord that I modified. Other pic is how the termination block on the southwire power reel works. Secured everything within an inch or two and the power watchdog is happy.


Let me know if you want a different pic, but, I have a late 2021 3400KD, imagine it'd be same as your in-progress 2022.


Jim
Attached Thumbnails
Click image for larger version

Name:	IMG_8520.jpg
Views:	75
Size:	317.1 KB
ID:	266360   Click image for larger version

Name:	IMG_8521.jpg
Views:	71
Size:	334.1 KB
ID:	266361  
__________________
2021 Dynamax Dynaquest XL 3400KD
2022 Aluma 8220H Tilt flatbed to carry:
2012 Jeep JKU Rubicon or slightly modded 2001 Jeep TJ
CyberShanks is offline   Reply With Quote
Old 12-03-2021, 05:15 PM   #10
Senior Member
 
Join Date: Jul 2020
Posts: 159
Quote:
Originally Posted by CyberShanks View Post
Other pic is how the termination block on the southwire power reel works.
Jim
So the top pic is the side of the power reel where the armored cable originally came out of? (right side to the rear of RV)?
__________________
2021 Dynaquest 3801TS
2023 Rubicon JLU Xtreme Recon
2020 Jeep Wrangler Limited Willys
MAC D is offline   Reply With Quote
Old 12-03-2021, 05:29 PM   #11
Senior Member
 
twp5253's Avatar
 
Join Date: May 2018
Posts: 444
The bottom of that device goes toward the coach. So, I suspect the armored cable, that looks like LiquidTight Conduit, goes into the coach.
__________________
2022 DynaQuest XL 3400KD CabOver, WD, Lithium Batteries, 4 190Watt Rigid Panels, extra inverter for AC operation w/o Genset.
twp5253 is offline   Reply With Quote
Old 12-03-2021, 05:41 PM   #12
Senior Member
 
Join Date: Jul 2020
Posts: 159
Yep, disconnect the Liquid Tight Conduit from the cord reel and wire to the cord with the male plug.

Then wire the female receptacle box to the cord reel.

You can then plug your surge protector in between the two - or not!

Here's another pic. It is a vertical picture, may be sideways...
Attached Thumbnails
Click image for larger version

Name:	20211203_153733.jpg
Views:	50
Size:	227.8 KB
ID:	266370  
__________________
2021 Dynaquest 3801TS
2023 Rubicon JLU Xtreme Recon
2020 Jeep Wrangler Limited Willys
MAC D is offline   Reply With Quote
Old 12-03-2021, 06:55 PM   #13
Senior Member
 
CyberShanks's Avatar
 
Join Date: May 2014
Location: Top of a hill (in Iowa) surrounded by corn.
Posts: 681
Ya, and for some reason my top pic is sideways. That is what it looks like under the steel cover on right side of the power reel. I didn't cut anything off of factory wire so that it technically could be put back the way it was, that is why they are sitting a bit weird.


Power watchdog input is at top and output is at bottom, due to the orientation in there it made most sense to mount it sideways in there to get ahold of the factory wires on the output side.


I had to buy 10 ft of 6/3 wire, so, if anyone else needs/wants to do this, I'll have some spare wire, as I only need about 2-3 ft tops.



Jim
__________________
2021 Dynamax Dynaquest XL 3400KD
2022 Aluma 8220H Tilt flatbed to carry:
2012 Jeep JKU Rubicon or slightly modded 2001 Jeep TJ
CyberShanks is offline   Reply With Quote
Old 12-03-2021, 07:02 PM   #14
Senior Member
 
Desert Boat's Avatar
 
Join Date: Jan 2021
Location: Fort Mill SC
Posts: 344
Quote:
Originally Posted by CyberShanks View Post
Question, I have the new hard-wired 50A Watchdog with EPO. I see that 6/3 wire is stated above with ground. What are people's thoughts on 6/2+8/1 with ground? Obviously the hots would be on 6 ga, neutral and ground on 8 ga. I see many heavy duty 50A dryer cords with this spec. What are thoughts?


Jim
Neutral has to be the same size as the hots, since it may have to carry the same current. I know the odds are that you will never be drawing 50 amps exclusively on one leg, but I don't cut corners with electrical wiring.
__________________
2021 Isata 5 28ss 4x2 / 2020 JLU Rubicon
Prior: 2016 Lance 1995 / Ram 1500 Eco Diesel
2012 Lance 1575 / 2015 Jeep JKU Rubicon
Desert Boat is offline   Reply With Quote
Old 12-03-2021, 07:09 PM   #15
Senior Member
 
CyberShanks's Avatar
 
Join Date: May 2014
Location: Top of a hill (in Iowa) surrounded by corn.
Posts: 681
I have correct wire on order and I'll fix it next week. Till then, I'm only plugged into 30A service at the house.



I've been doing much reading on this, I feel that with 240V, the wire I have would be fine, problem starts due to 120V. With 240V, the neutral only carries current difference between the 2 hot legs, since I am currently using a dryer cord, it's always running 240V and likely spreading the load pretty equally across the legs. With the 120V, there's more of a chance of a single leg going full 50A, which would put full 50A load on the neutral. (I believe I get it now, please correct me if I'm wrong here)



Why we have these forums, and certainly why I asked the question.



Thanks,
Jim
__________________
2021 Dynamax Dynaquest XL 3400KD
2022 Aluma 8220H Tilt flatbed to carry:
2012 Jeep JKU Rubicon or slightly modded 2001 Jeep TJ
CyberShanks is offline   Reply With Quote
Old 12-04-2021, 07:22 AM   #16
Senior Member
 
Join Date: Jul 2020
Posts: 159
I would suggest you get a certified electrician out to get it wired up properly. You're dealing with some serious power and fire hazard if not done correctly. The electrician could get you fixed up and give you some education rather quickly.

All the wiring should be in conduit, junction boxes all properly anchored with the correct fittings. No exposed wiring.

Also, I would want to be able to bypass the surge protector in case of a failure. That's why we were discussing the addition of an outlet and male plug.

Just my HO. I'm concerned about the well being of you and your rig.
__________________
2021 Dynaquest 3801TS
2023 Rubicon JLU Xtreme Recon
2020 Jeep Wrangler Limited Willys
MAC D is offline   Reply With Quote
Old 12-04-2021, 11:07 AM   #17
Senior Member
 
twp5253's Avatar
 
Join Date: May 2018
Posts: 444
I would suggest the addition of dielectric grease at the connections. https://www.amazon.com/CRC-6113-Mari...8633695&sr=8-7
This one is great because you can pump in some grease into the big holes and then put the wire in and all is coated. Leave some of it coating everything.
Another suggestion is to go back and check connections are tight. Sometimes the copper wire settles a bit and the last thing you want is a loose connection. This happens more often with stranded wire which is the best because it carries more current. Electrons like to travel on the skin of the copper and that is why welding cables are stranded...very fine strands! Don't break the fitting, just re-check that it is tight after a couple of days/weeks. I found my main breaker panel in the GarageMahal had a loose hot wire after a couple of weeks. My inspector said my electrical work was the best he has seen so you can do the job, just be meticulous and do your research.
__________________
2022 DynaQuest XL 3400KD CabOver, WD, Lithium Batteries, 4 190Watt Rigid Panels, extra inverter for AC operation w/o Genset.
twp5253 is offline   Reply With Quote
Old 12-04-2021, 11:15 AM   #18
Senior Member
 
twp5253's Avatar
 
Join Date: May 2018
Posts: 444
Quote:
Originally Posted by Desert Boat View Post
Neutral has to be the same size as the hots, since it may have to carry the same current. I know the odds are that you will never be drawing 50 amps exclusively on one leg, but I don't cut corners with electrical wiring.
For everyone following along, Neutral = Common Normally white and must be same size as the hots which often are black and red.

Ground, is usually green or bare. In a main fuse box they are often treated the same and connect up to the same connection bars. In a Sub Panel, they are separate with ground going down to the copper rod in the ground and/or back to main panel green. Local codes sometimes call for a separate grounding rod at the sub panel. I had to learn all this once my GarageMahal was ordered and there are no descent electricians where my vacation home is located.
__________________
2022 DynaQuest XL 3400KD CabOver, WD, Lithium Batteries, 4 190Watt Rigid Panels, extra inverter for AC operation w/o Genset.
twp5253 is offline   Reply With Quote
Old 12-10-2021, 03:09 PM   #19
Senior Member
 
CyberShanks's Avatar
 
Join Date: May 2014
Location: Top of a hill (in Iowa) surrounded by corn.
Posts: 681
FWIW, I switched over to the portable unit that is now plugged into a freshly installed hard-wired outlet in the front bay. Happy Friday



Jim
__________________
2021 Dynamax Dynaquest XL 3400KD
2022 Aluma 8220H Tilt flatbed to carry:
2012 Jeep JKU Rubicon or slightly modded 2001 Jeep TJ
CyberShanks is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 03:18 AM.