2009 Sabre 31RETS-6 Heating ducts

Hi, we are having a problem with heat distribution in our Sabre. The two heating ducts towards the rear of the trailer, living area and part of kitchen, have a good flow rate The ones towards the front, bedroom, bathroom and entrance area, are very poor. There is hot air getting to them but not at any great flow rate.

Looking at the position of the furnace, it appears that a duct comes from the furnace to the centre of the kitchen then branches via a "T" to the back and front of the trailer. Obvious first though was a blockage after the T towards the back of the trailer. Although I wasn't able to see through the duct work to check for a blockage, there was no apparent block when I pushed a steel tape measure from the back ducts to the front, likewise a flashlight placed in the duct-work showed no blockage.

Any thoughts?

ex-egll
ex-egll is offline   Reply With Quote
Old 01-20-2014, 01:13 PM   #2
Senior Member
 
rjf7g's Avatar
 
Join Date: May 2012
Posts: 147
Has this been the case since 2009 or is this a new problem? I had a similar issue with my Gulf Stream and the dealer installed another duct in the front bedroom.

Even with the new duct, we were still getting too much heat in the rear bedroom, so I bought a vent that had a damper on it. The air will take the path of least resistance, so this helped with that issue.
__________________
***********************************************
2006 Palomino Puma 27FQ Bunkhouse
2007 Gulfstream Innsbruck 36FRS Park Trailer
rjf7g is offline   Reply With Quote
Old 01-20-2014, 05:11 PM   #3
Member
 
Join Date: Mar 2013
Posts: 69
Thanks for the response! I must admit I have never checked this out before, for all I know it could have been like it from day 1.

What really confuses me is the fact that both vent 1 and vent 2 are equidistant (about 18") from the T with no apparent blockage any where, yet the airflow at vent 1 is about 10 times greater than at vent 2. All I can think of now is that there is a massive leak towards the front of the trailer.





ex-egll
ex-egll is offline   Reply With Quote
Old 01-21-2014, 07:22 AM   #4
Senior Member
 
amxpress's Avatar
 
Join Date: Nov 2007
Location: Clayton, NC
Posts: 695
Seems to be a common concern with 5th wheels. At nite, I placed 2 magnetic register covers over the registers in the living room and kitchen which increased the volume coming out in the bathroom and bedroom.
I ended up replacing the registers with ones that I could close the louvers, purchased at Lowe's.
__________________
2013 Palomino Columbus 320RS
2007 Dodge RAM 2500 6.7 Cummins
Reese 15K manual slider
Prodigy
M.I.L. in Florida for good!!
amxpress is offline   Reply With Quote
Old 01-21-2014, 08:07 AM   #5
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Quote:
Originally Posted by ex-egll View Post
Hi, we are having a problem with heat distribution in our Sabre. The two heating ducts towards the rear of the trailer, living area and part of kitchen, have a good flow rate The ones towards the front, bedroom, bathroom and entrance area, are very poor. There is hot air getting to them but not at any great flow rate.

Looking at the position of the furnace, it appears that a duct comes from the furnace to the centre of the kitchen then branches via a "T" to the back and front of the trailer. Obvious first though was a blockage after the T towards the back of the trailer. Although I wasn't able to see through the duct work to check for a blockage, there was no apparent block when I pushed a steel tape measure from the back ducts to the front, likewise a flashlight placed in the duct-work showed no blockage.

Any thoughts?

ex-egll
Ex-eg
My sabre has the same issue.
We "sabre factory" and I think we have a solution.

Blocking vents does not solve the issue.

I'll send you a pm with my contact info.



TURBS

golf cart safety instructor
TURBS is offline   Reply With Quote
Old 01-21-2014, 08:49 AM   #6
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Quote:
Originally Posted by rjf7g View Post
Has this been the case since 2009 or is this a new problem? I had a similar issue with my Gulf Stream and the dealer installed another duct in the front bedroom.

Even with the new duct, we were still getting too much heat in the rear bedroom, so I bought a vent that had a damper on it. The air will take the path of least resistance, so this helped with that issue.
My 11' has the same issue.
At the goshen rally I found that a 10' did not have the issue and a 12' that also did not have an issue.

The factory tech's and I discussed the problem and think we've found the problem and a cure.

TURBS

golf cart safety instructor
TURBS is offline   Reply With Quote
Old 01-21-2014, 12:34 PM   #7
Member
 
Join Date: Mar 2013
Posts: 69
Again, thanks for the comments, and to f1100turbo for the call. Have got a couple of ideas to work on now. I'll update after I've played around a little
ex-egll is offline   Reply With Quote
Old 01-22-2014, 07:27 AM   #8
Junior Member
 
Join Date: Aug 2013
Posts: 6
Let us know what may be the fix of this problem because I don't get much heat up in our bedroom either. Thanks
Woodchuck88 is offline   Reply With Quote
Old 01-22-2014, 07:41 AM   #9
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Quote:
Originally Posted by Woodchuck88 View Post
Let us know what may be the fix of this problem because I don't get much heat up in our bedroom either. Thanks
Pm sent.

TURBS

dog wisperer
TURBS is offline   Reply With Quote
Old 01-22-2014, 08:06 AM   #10
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
To let everyone know were going to be doing the modification soon with pictures to fix this issue.

TURBS

dog wisperer
TURBS is offline   Reply With Quote
Old 01-22-2014, 11:30 AM   #11
Junior Member
 
canmannc's Avatar
 
Join Date: Nov 2012
Location: Salty Shores, NC
Posts: 28
Basement Ducts

Don't forget...on my 2006 Sandpiper 335RLT 5er there is also a duct going to the basement (storage compartment). It does well to keep the water filter, tanks and pipes and other stuff I keep down there from freezing. However, it does reduce the flow in the bedroom register. My fix is a small ceramic 750/1500 watt electric heater from Lowes.

Turbs, I am looking fwd to see your mod...Thanks for sharing
Attached Images
 
__________________
2006 Sandpiper 335RTL
2005 2500 HD Duramax w/hypertech programer
DW and Sallie Dog
New addition "Katmandu" rescue cat from Bear Creek Campground, Asheville on Christmas Day 2013
Camped in 2014 = lost count...but over 40...more to come!
canmannc is offline   Reply With Quote
Old 01-26-2014, 07:47 PM   #12
Member
 
Join Date: Mar 2013
Posts: 69
Partial Update

I emptied out the storage area and found the outlet for the hot air. It had been damaged by pushing stuff into the area repeatedly. Effectively the vent was wide open. In addition I looked at the vent fitting and it protruded almost 2" into the duct work. The duct work itself was only about 2" deep; this effectively blocked of a great amount of the air flow. As Turbs pointed out, the routing of the duct work is pretty haphazard, it comes out of the kitchen area, under the storage area with one vent in it, then across the rest of the storage area up a flexible tube to more duct-work that goes back across the top of the storage area to the bedroom vent and finally the bathroom.

I plan to move the vertical pipe from the front of the storage area, back to where the vent is, and block off the unused duct-work.

Closing off the vent in the storage area restored some of the airflow in the bedroom / bathroom, but I think there is room for improvement.
ex-egll is offline   Reply With Quote
Old 01-27-2014, 10:35 AM   #13
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Quote:
Originally Posted by ex-egll View Post
Partial Update

I emptied out the storage area and found the outlet for the hot air. It had been damaged by pushing stuff into the area repeatedly. Effectively the vent was wide open. In addition I looked at the vent fitting and it protruded almost 2" into the duct work. The duct work itself was only about 2" deep; this effectively blocked of a great amount of the air flow. As Turbs pointed out, the routing of the duct work is pretty haphazard, it comes out of the kitchen area, under the storage area with one vent in it, then across the rest of the storage area up a flexible tube to more duct-work that goes back across the top of the storage area to the bedroom vent and finally the bathroom.

I plan to move the vertical pipe from the front of the storage area, back to where the vent is, and block off the unused duct-work.

Closing off the vent in the storage area restored some of the airflow in the bedroom / bathroom, but I think there is room for improvement.
Dont forget pictures!

Sounds good!

TURBS

dog wisperer
TURBS is offline   Reply With Quote
Old 01-27-2014, 11:55 AM   #14
Member
 
Join Date: Mar 2013
Posts: 69
Thanks for the reminder, I would probably totally forgotten to take any.

Just need to make up a shopping list now. The plan is to run flexi-pipe straight up from the storage floor vent to the overhead ducting, block off both the floor and overhead ducting where the current flexi-pipe runs and maybe put an additional, adjustable vent in the overhead duct work for the storage area. We very rarely camp anywhere we'd need to use heat in that area so I will probably not bother.

Once I start I will look at the feasibility of removing the rear wall in the storage area, and if it is simple I will try to put the vertical flexi pipe there so as not to reduce space.
ex-egll is offline   Reply With Quote
Old 01-27-2014, 03:19 PM   #15
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Quote:
Originally Posted by ex-egll View Post
Thanks for the reminder, I would probably totally forgotten to take any.

Just need to make up a shopping list now. The plan is to run flexi-pipe straight up from the storage floor vent to the overhead ducting, block off both the floor and overhead ducting where the current flexi-pipe runs and maybe put an additional, adjustable vent in the overhead duct work for the storage area. We very rarely camp anywhere we'd need to use heat in that area so I will probably not bother.

Once I start I will look at the feasibility of removing the rear wall in the storage area, and if it is simple I will try to put the vertical flexi pipe there so as not to reduce space.
Can wait to see !

TURBS

dog wisperer
TURBS is offline   Reply With Quote
Old 02-01-2014, 09:38 PM   #16
Member
 
Join Date: Dec 2012
Posts: 71
I had a problem with my Sabre furnace not heating well and short cycling the burner. Had the dealer check it out and they removed over 20 feet of extra flexible duct work. When it was built if there was a fairly straight 3 foot run they would have 6 or more feet of duct work snaked around instead of cutting to fit. Furnace now works 100% better, as it should.
okietom is offline   Reply With Quote
Old 02-02-2014, 02:23 PM   #17
Member
 
Join Date: Mar 2013
Posts: 69
The Plot Thickens

Today I decided to do some further investigating into the heating issue, specifically the ductwork around the furnace area. I decided on the hi-tech approach, and stuck my digital camera into the ductwork. The results were a little surprising. They are shown below in a plan sketch of the ducting.



So it now seems that other than taking the base off the rig and mosifying the ductwork, the best solution is to:

1> Put adjustable registers into the living area and close them down at night,
and;
2> Clean up the ductwork in the storage area to give a smoother airflow.


ex-egll
ex-egll is offline   Reply With Quote
Reply

Tags
heating, sabre

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 02:29 PM.