AC power

We are cosidering buying a Rockwood 8296SS. Is the 13,500 btu AC enough or should we upgrade to the 15,000 btu? We live and camp in FL.
Thanks
Time2Tow is offline   Reply With Quote
Old 08-13-2010, 12:13 PM   #2
Senior Member
 
DAISY BOYKIN's Avatar
 
Join Date: Jun 2010
Location: SUNSHINE STATE
Posts: 1,769
Send a message via Skype™ to DAISY BOYKIN
By all means, upgrade!

For what little it cost between the 13.5 BTU and the 15K BTU, upgrade.
If you are coming to Florida (I live here) UPGRADE, UPGRADE, UPGRADE !!!!!! I promise you that you will not be sorry.


Sid & HRH DAISY
DAISY BOYKIN is offline   Reply With Quote
Old 08-13-2010, 12:52 PM   #3
Member
 
Join Date: Aug 2010
Posts: 39
Quote:
Originally Posted by DAISY BOYKIN View Post
For what little it cost between the 13.5 BTU and the 15K BTU, upgrade.
If you are coming to Florida (I live here) UPGRADE, UPGRADE, UPGRADE !!!!!! I promise you that you will not be sorry.


Sid & HRH DAISY
Thank you for the input. We also live in FL, (Lutz which borders Tampa) and we were pretty sure that was the right way to go. Stay cool!
Time2Tow is offline   Reply With Quote
Old 08-13-2010, 01:16 PM   #4
Senior Member
 
Join Date: Jul 2010
Posts: 7,948
Quote:
Originally Posted by Thomas Kolessar View Post
We are cosidering buying a Rockwood 8296SS. Is the 13,500 btu AC enough or should we upgrade to the 15,000 btu? We live and camp in FL.
Thanks
Yes the 15,000 BTU AC is a must!
Iggy is offline   Reply With Quote
Old 08-13-2010, 02:10 PM   #5
Senior Member
 
NWJeeper's Avatar
 
Join Date: Aug 2008
Location: Enumclaw, WA
Posts: 2,615
YES, upgrade. Beter to have it and not need it than not have it and wished you had.

We only ordered one AC on our rig when new as we do 90% of our camping in conditions that require heat and I didn't want to carry the weight or spend the money on a 2nd AC. After our maiden voyage to Arizona and Utah I was wishing I had gotten the 2nd one.

Go with the bigger AC, every time!
__________________
"I can fix it, and if I can't fix it, I can fix it so no one can fix it!"
Ed & Wendy
2009 Georgetown 378TS | 1998 Jeep Wrangler | 1998 Skeeter ZX202C
Nights camped in 2009: 53 | Nights camped in 2010: 55
www.nwjeepn.com
NWJeeper is offline   Reply With Quote
Old 08-13-2010, 02:16 PM   #6
Member
 
Join Date: Aug 2010
Posts: 39
Quote:
Originally Posted by NWJeeper View Post
YES, upgrade. Beter to have it and not need it than not have it and wished you had.

We only ordered one AC on our rig when new as we do 90% of our camping in conditions that require heat and I didn't want to carry the weight or spend the money on a 2nd AC. After our maiden voyage to Arizona and Utah I was wishing I had gotten the 2nd one.

Go with the bigger AC, every time!
I appreciate the advice. The decision has been made to go with the 15,000.
Thanks
Time2Tow is offline   Reply With Quote
Old 09-01-2010, 08:54 AM   #7
Senior Member
 
2manytoyz's Avatar
 
Join Date: Sep 2006
Location: Central FL
Posts: 134
Too late, but I would have recommended the 13,500. Reason being, the 15K A/C unit requires a larger generator to run it. This may not ever be a concern for you if you don't boondock.

The Yamaha EF2400iS is the lightest, quiet series generator, capable of reliably running a 13,500 BTU A/C unit. The next sized generator, a 3KW, DOUBLEs the weight (70 lbs vs 140 lbs), and is still too small for the 15K A/C unit! Many have reported a 3.5KW generator is also too small.

I'm in FL also, and our camper is part of our evacuation plan, as is the generator.

2manytoyz - Yamaha EF2400iS Generator
__________________
Robert & Dawn
2015 Forest River Georgetown 328TS
2006 Jeep Wrangler Unlimited TOAD
https://www.2manytoyz.com/
2manytoyz is offline   Reply With Quote
Old 09-01-2010, 08:59 AM   #8
Senior Member
 
Join Date: Jul 2010
Posts: 7,948
Quote:
Originally Posted by 2manytoyz View Post
Too late, but I would have recommended the 13,500. Reason being, the 15K A/C unit requires a larger generator to run it. This may not ever be a concern for you if you don't boondock.

The Yamaha EF2400iS is the lightest, quiet series generator, capable of reliably running a 13,500 BTU A/C unit. The next sized generator, a 3KW, DOUBLEs the weight (70 lbs vs 140 lbs), and is still too small for the 15K A/C unit! Many have reported a 3.5KW generator is also too small.

I'm in FL also, and our camper is part of our evacuation plan, as is the generator.

2manytoyz - Yamaha EF2400iS Generator
You are true that the 15K will draw more current but it is not much.
The NEW 15K pulls 16 amps and the 13.5K about an amp less. That is minor but if you have a generator close to max load already yes it is an issue. I predict that all roof AC on RV will be 15K soon.
Iggy is offline   Reply With Quote
Old 09-01-2010, 11:16 AM   #9
Member
 
Join Date: Aug 2010
Posts: 39
Thanks for the additional information. I do not use a generator when camping but I appreciate bringing this into the discussion. Getting different viewpoints is why I like these forums. Living in FL and having been through some close calls with hurricanes and losing power for a few days, I do now have a generator but never considered it and my camper as part of an evacuation plan. I actually considered it more of my back-up plan for a place to stay if the house got damaged. Since my generator is still in the box, I think I will check it for it'spower output. It is the peek of hurricane season.
Time2Tow is offline   Reply With Quote
Old 09-01-2010, 11:30 AM   #10
Senior Member
 
2manytoyz's Avatar
 
Join Date: Sep 2006
Location: Central FL
Posts: 134
It's not about the running current, but rather the starting current. It takes upwards of 5 times the running current to start the compressor.

Most Ammeters are too slow to measure this. I purchased a Fluke meter, with an "In-Rush" feature.

Here's the actual startup current for my 13,500 BTU A/C unit:



Here's the running current once started:



Here's the tricky part, the generator manufacturers don't give you all the specs. But neither do the folks that make the products that plug into the generators.

My generator is 2400 Watts. 2400W for how long? 2000 Watts continuous. Hayes Equipment put a load on the generator, and reported it can handle a 3000W load for 10 seconds. How much can it handle for the split second needed to spin a motor? FWIW, the 2400W, 2800W, and 3000W Yamaha generators all use the same sized motor.

From my testing, my generator can handle a 50A load, but not a 53.8A load (my air compressor rated at 15A):



So it's already very near its limit. In that split second, the RPMs bump on the generator, the A/C EASILY starts, and the RPMs settle down to about 2/3 throttle. But when trying to start the air compressor, the compressor slowly rolls over, the generator grunts for 10 seconds, then finally indicates "overload".

My website is one of the very few that has actual testing of the Yamaha EF2400iS (I make nothing for this!). I've talked to literally thousands of people on this topic. Many I've talked with have tried unsuccessfully to run a 15K A/C unit with generators. Zero have had success with a 3KW or smaller generator.
__________________
Robert & Dawn
2015 Forest River Georgetown 328TS
2006 Jeep Wrangler Unlimited TOAD
https://www.2manytoyz.com/
2manytoyz is offline   Reply With Quote
Old 09-01-2010, 11:54 AM   #11
Senior Member
 
NWJeeper's Avatar
 
Join Date: Aug 2008
Location: Enumclaw, WA
Posts: 2,615
One Dometic owners manual I found showed a start up load for a 13.5K AC at 54 amps and for the 15K unit 71 amps. Running amps were very close however, less than 2 amps.
__________________
"I can fix it, and if I can't fix it, I can fix it so no one can fix it!"
Ed & Wendy
2009 Georgetown 378TS | 1998 Jeep Wrangler | 1998 Skeeter ZX202C
Nights camped in 2009: 53 | Nights camped in 2010: 55
www.nwjeepn.com
NWJeeper is offline   Reply With Quote
Old 09-01-2010, 11:57 AM   #12
Senior Member
 
2manytoyz's Avatar
 
Join Date: Sep 2006
Location: Central FL
Posts: 134
Quote:
Originally Posted by Time2Tow View Post
Thanks for the additional information. I do not use a generator when camping but I appreciate bringing this into the discussion. Getting different viewpoints is why I like these forums. Living in FL and having been through some close calls with hurricanes and losing power for a few days, I do now have a generator but never considered it and my camper as part of an evacuation plan. I actually considered it more of my back-up plan for a place to stay if the house got damaged. Since my generator is still in the box, I think I will check it for it'spower output. It is the peek of hurricane season.
I learned my lesson in 1995. Hurricane Erin, a lowly Cat 1 storm, thumped us. No power for 3 days, trashed all my trees.



Then in 2004, Frances and Jeanne thumped us 3 weeks apart. We evacuated in our MH (had a 36' Class A back then) to GA, then returned afterwards. It ripped shingles off the roof, but the paper was still intact. The roof was temporarily patched, then Jeanne showed up 3 weeks later. We stayed for that one. The patch held, but more shingles ripped off, pouring water into the master bedroom. I patched the damage the next day. No power, so we stayed in the MH for a few days, running the generator, living in comfort.

Coworkers in the nearby area, were without power for 18 days. One had a conventional generator, which consumes about 1.5 gallons per hour. The other had a Honda 2KW, which consumes about 1 gallon every 8 hours. Mine present generator consumes about 1.5 gallons every 8 hours or 4.5 gallons per day (1/4 load). A little math...

18 days x 24 hours x 1.5 gallons = 648 gallons!

18 days, x 4.5 gallons per day (Yamaha) = 81 gallons.

A conventional generator runs at a constant speed to make 60Hz. An inverter type generator makes 60Hz electronically from idle. The motor only runs as fast as the load demands, which can significantly reduce the fuel consumption.

During an outage at home, I will run 2 refrigerators, and a 5000 BTU A/C unit (window shaker) to cool one room. Not enough resources to cool an entire house. But I can make a single room 72 degrees, even in the middle of a FL Summer!

Measured #s:

Each fridge running ~140W-150W, defrost cycle ~600W
5000 BTU A/C unit running ~600W

So for the most part, my generator runs my critical loads from idle (1/4 throttle). Whisper quiet at 53 dB, very thrifty on resources. When storms approach, I fill ten 5 gallon gas cans. If those run out, we leave!

I tell you the story of my two coworkers as that was the lesson that convinced me to part ways with conventional generators (I had a Coleman 4200W), and now have the smaller Yamaha EF2400iS. It not only takes care of the camper, but also emergency power at home.

Didn't want to hijack the thread, but thought you might find the info useful.
__________________
Robert & Dawn
2015 Forest River Georgetown 328TS
2006 Jeep Wrangler Unlimited TOAD
https://www.2manytoyz.com/
2manytoyz is offline   Reply With Quote
Old 09-01-2010, 12:03 PM   #13
Senior Member
 
Join Date: Jul 2010
Posts: 7,948
Why are you bring up electrical theory when all was asked if he should get a 13.5K AC unit or a 15K unit. I have a electrical degree and have been in the business for over 42 years so please it is not necessary to explain starting amp and running amps to me.
Thanks for a great demo with pictures.
Iggy is offline   Reply With Quote
Old 09-01-2010, 12:05 PM   #14
Senior Member
 
NWJeeper's Avatar
 
Join Date: Aug 2008
Location: Enumclaw, WA
Posts: 2,615
Thanks Robert and your story brings a good point to light about buying generators. The difference in cost of gas over a period of time will pay for that more expensive Yamaha or Honda generator vs buying an auto parts store cheapo (loud) generator which are usually not any where near the same quality either.
__________________
"I can fix it, and if I can't fix it, I can fix it so no one can fix it!"
Ed & Wendy
2009 Georgetown 378TS | 1998 Jeep Wrangler | 1998 Skeeter ZX202C
Nights camped in 2009: 53 | Nights camped in 2010: 55
www.nwjeepn.com
NWJeeper is offline   Reply With Quote
Old 09-01-2010, 12:06 PM   #15
Senior Member
 
2manytoyz's Avatar
 
Join Date: Sep 2006
Location: Central FL
Posts: 134
Quote:
Originally Posted by NWJeeper View Post
One Dometic owners manual I found showed a start up load for a 13.5K AC at 54 amps and for the 15K unit 71 amps. Running amps were very close however, less than 2 amps.
That's great, some useful (to me) numbers! I couldn't find anything on the 15K unit, so I appreciate the info.

A hard start kit will help spin an A/C unit that's marginal by phase shifting, but wouldn't help with the 15K unit. That's a big difference in start up current!
__________________
Robert & Dawn
2015 Forest River Georgetown 328TS
2006 Jeep Wrangler Unlimited TOAD
https://www.2manytoyz.com/
2manytoyz is offline   Reply With Quote
Old 09-01-2010, 12:20 PM   #16
Senior Member
 
2manytoyz's Avatar
 
Join Date: Sep 2006
Location: Central FL
Posts: 134
Quote:
Originally Posted by Iggy View Post
Why are you bring up electrical theory when all was asked if he should get a 13.5K AC unit or a 15K unit. I have a electrical degree and have been in the business for over 42 years so please it is not necessary to explain starting amp and running amps to me.
Thanks for a great demo with pictures.
I bring it up because you said: "You are true that the 15K will draw more current but it is not much. The NEW 15K pulls 16 amps and the 13.5K about an amp less. That is minor but if you have a generator close to max load already yes it is an issue."

Again, running current isn't the issue. Starting current is. If he ever plans on running his A/C unit on a generator, the size of the A/C unit matters!

I didn't bring up theory, I showed you ACTUAL numbers. That's the problem with most discussions, lots of theories, very few facts.

There's no telling who the audience is, nor who the person talking is. I've been in the business a while too. And 'twasn't a lesson for you, but rather the OP, or anyone else considering a 13.5K vs 15K. The idea of getting a tad more cooling now sounds great. But having to lug around a $2K generator @ 200 lbs, might be an issue later if wanting to visit BLM land, or having to bail out during storm.
__________________
Robert & Dawn
2015 Forest River Georgetown 328TS
2006 Jeep Wrangler Unlimited TOAD
https://www.2manytoyz.com/
2manytoyz is offline   Reply With Quote
Reply

Tags
rockwood


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 06:59 AM.