Old 05-22-2020, 07:36 PM   #21
Junior Member
 
Join Date: May 2020
Posts: 13
It is the 120 volt 58 amp
__________________

Hatteras67 is offline   Reply With Quote
Old 05-22-2020, 07:36 PM   #22
Junior Member
 
Join Date: May 2020
Posts: 13
Quote:
Originally Posted by CHICKDOE View Post
what model generator do you have? i did an online search and if i understand what i saw there are generators rated at 7000 watts configured as single phase generators at either 60 amps @120 volts or 30 amps @ 240 volts. do you by chance have a 30 amp 240 volt model? get the model number of your generator and confirm what you have.
Itís the 120 volt 58 amp
__________________

Hatteras67 is offline   Reply With Quote
Old 05-22-2020, 07:41 PM   #23
Junior Member
 
Join Date: May 2020
Posts: 13
Quote:
Originally Posted by CHICKDOE View Post
what model generator do you have? i did an online search and if i understand what i saw there are generators rated at 7000 watts configured as single phase generators at either 60 amps @120 volts or 30 amps @ 240 volts. do you by chance have a 30 amp 240 volt model? get the model number of your generator and confirm what you have.
7hgjae-2132
Hatteras67 is offline   Reply With Quote
Old 05-22-2020, 07:53 PM   #24
far north Alabama
 
formerFR's Avatar
 
Join Date: Jan 2017
Location: far north AL
Posts: 2,801
it's not a 'single' breaker, but actually TWO individual 30amp breakers, though only ONE trip handle, shown as '30amp'....which means up to 60amps at 120v between the two.
With a 58amp 7000kw Onan generator, it makes perfect sense.

basically, up to 29amps goes to one line, and upt to 29amps to the other, both fed back to the different two 'sides' of your Main Panel.

Generators that don't output 240v are used since your RV doesn't NEED 240v power, only 120v to your Main Panel. Now, while you might argue that then 'why' do you need to plug into a 50amp 240v campground outlet - it's because the electrical grid is designed differently than a generator. With the grid, you won't find a 100amp 120v outlet, so a more 'normal' 50amp 240v outlet is the 'common' campground or rv park outlet for larger RVs. A single 120v 100amp sized wire would be SO THICK that it would make your shore cord unmanageable.

The same idea surrounds the generator's output with TWO breakers - it reduces the size of the wires needed that lead back to your Main Panel, which sometimes can be at opposite ends of the coach, especially in diesel models. Even though it might seem odd that the generator's breaker only shows 'one' breaker handle, it actually is not that uncommon, but the fact that you don't 'see' that other breaker might lead one to believe that the generator only produces the power of that single breaker.
__________________

The Turners
'14 Thor Palazzo 33.3 compact diesel
KingTailgater2 Dish, 100w/5amps roof SOLAR, BlueOx, 100,000+mi since '14... US, Alaska, and Canada... GA, NC, now N AL : )
formerFR is online now   Reply With Quote
Old 05-22-2020, 08:01 PM   #25
Senior Member
 
Join Date: Jun 2015
Location: payson, az
Posts: 2,452
i can certainly accept what FORMERFR said above.
__________________
2015 cardinal model 3825fl
2015 dodge ram 3500 dually
CHICKDOE is offline   Reply With Quote
Old 05-22-2020, 08:15 PM   #26
Junior Member
 
Join Date: May 2020
Posts: 13
Quote:
Originally Posted by formerFR View Post
it's not a 'single' breaker, but actually TWO individual 30amp breakers, though only ONE trip handle, shown as '30amp'....which means up to 60amps at 120v between the two.
With a 58amp 7000kw Onan generator, it makes perfect sense.

basically, up to 29amps goes to one line, and upt to 29amps to the other, both fed back to the different two 'sides' of your Main Panel.

Generators that don't output 240v are used since your RV doesn't NEED 240v power, only 120v to your Main Panel. Now, while you might argue that then 'why' do you need to plug into a 50amp 240v campground outlet - it's because the electrical grid is designed differently than a generator. With the grid, you won't find a 100amp 120v outlet, so a more 'normal' 50amp 240v outlet is the 'common' campground or rv park outlet for larger RVs. A single 120v 100amp sized wire would be SO THICK that it would make your shore cord unmanageable.

The same idea surrounds the generator's output with TWO breakers - it reduces the size of the wires needed that lead back to your Main Panel, which sometimes can be at opposite ends of the coach, especially in diesel models. Even though it might seem odd that the generator's breaker only shows 'one' breaker handle, it actually is not that uncommon, but the fact that you don't 'see' that other breaker might lead one to believe that the generator only produces the power of that single breaker.
Thank you for the clarification.
__________________

Hatteras67 is offline   Reply With Quote
Reply

Tags
generator, wiring

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 08:13 PM.


×