PI surge protector wont turn on power

Installed PI surge protector with remote display,when plugged in to house,getting 123 60H E-0. When I plug in to new Boily gen set it reads e-2 "open ground" and will not turn on power. Using proper cord,with 30 amp 3 prong end. Tried with adapter plugged in to reg outlet on gen set,tripped power on gen set. In the instruction book from PI,it states "do not plug in to inverter" the Boily is an inverter gen. Is this the problem? Others must be using inverter type gen sets,

Thought to call customer serv. at PI,but sat 5:50,too late,so thought I would pick Y'all's brains first! Help !
Rolling buckeye is offline   Reply With Quote
Old 04-27-2013, 04:59 PM   #2
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Ground your gennie with a rod stuck in the ground and wired to your gennie.

Most gennies have a wing nut and a post to attach the wite to.
TURBS is offline   Reply With Quote
Old 04-27-2013, 05:01 PM   #3
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Basically your gennie has no earth ground unless you do this.

Click image for larger version

Name:	ForumRunner_20130427_170131.jpg
Views:	167
Size:	38.4 KB
ID:	29091
TURBS is offline   Reply With Quote
Old 04-27-2013, 05:02 PM   #4
Phat Phrog Stunt Team
 
Rolling buckeye's Avatar
 
Join Date: Feb 2013
Posts: 1,330
Quote:
Originally Posted by f1100turbo View Post
Ground your gennie with a rod stuck in the ground and wired to your gennie.

Most gennies have a wing nut and a post to attach the wite to.
Thanks Turbs ! I'll go try! U Da Man !
Rolling buckeye is offline   Reply With Quote
Old 04-27-2013, 05:03 PM   #5
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Drive your rod into the ground a foot or so then attach a wire with a hose clamp to it.
Then hook loose end to gennie ground lug as pictured above.


Turbs
TURBS is offline   Reply With Quote
Old 04-27-2013, 05:03 PM   #6
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
All I got to say is BBC!
TURBS is offline   Reply With Quote
Old 04-27-2013, 05:37 PM   #7
Senior Member
 
fonzie's Avatar
 
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 4,167
I don't think grounding your generator to a ground rod will make a difference. In a normal house supply the ground and neutral are tied together in the electrical panel but not in the generator (not mine which is a Yamaha) So either you bypass your PI surge protector on your remote display or you need to do an adapter. See attached.
Attached Files
File Type: pdf Special Generator Pigtail Instructions.pdf (132.6 KB, 71 views)
__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2019 F350 Ruby Red 6.7l diesel 3.31 axle electronic locker
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2014 (18) 2015 (18) 2016 (36) 2017 (32) 2018 (42) 2019 (28) 2020 (35)
fonzie is offline   Reply With Quote
Old 04-27-2013, 05:41 PM   #8
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Quote:
Originally Posted by fonzie View Post
I don't think grounding your generator to a ground rod will make a difference. In a normal house supply the ground and neutral are tied together in the electrical panel but not in the generator (not mine which is a Yamaha) So either you bypass your PI surge protector on your remote display or you need to do an adapter. See attached.
Your house power is also grounded to earth.


My EMS showed same fault till I earth grounded my gennie.
TURBS is offline   Reply With Quote
Old 04-27-2013, 05:43 PM   #9
Phat Phrog Stunt Team
 
Rolling buckeye's Avatar
 
Join Date: Feb 2013
Posts: 1,330
Quote:
Originally Posted by f1100turbo View Post
Drive your rod into the ground a foot or so then attach a wire with a hose clamp to it.
Then hook loose end to gennie ground lug as pictured above.

Turbs
Roger . These are my connections. Still E2-PE2

Click image for larger version

Name:	image-1319300341.jpg
Views:	205
Size:	47.4 KB
ID:	29097

Opened panel on front of Boily, n checked,ground bolt I att. to is wired to grnd o rec's and to gen frame. ???
Attached Thumbnails
Click image for larger version

Name:	image-528266721.jpg
Views:	107
Size:	53.0 KB
ID:	29096  
Rolling buckeye is offline   Reply With Quote
Old 04-27-2013, 06:03 PM   #10
Phat Phrog Stunt Team
 
Rolling buckeye's Avatar
 
Join Date: Feb 2013
Posts: 1,330
Ok bypass worked, but darn ! Would have been nice to monitor gen power too!

Next Problem.....

Click image for larger version

Name:	image-2029765714.jpg
Views:	206
Size:	47.4 KB
ID:	29103

Aaaaaaaa. BBC .... Box ...... EMPTY !! The HORROR ! What do I do now !

Beerun !
Rolling buckeye is offline   Reply With Quote
Old 04-27-2013, 06:04 PM   #11
Phat Phrog Stunt Team
 
Rolling buckeye's Avatar
 
Join Date: Feb 2013
Posts: 1,330
Quote:
Originally Posted by fonzie View Post
I don't think grounding your generator to a ground rod will make a difference. In a normal house supply the ground and neutral are tied together in the electrical panel but not in the generator (not mine which is a Yamaha) So either you bypass your PI surge protector on your remote display or you need to do an adapter. See attached.
Thanks fonzie !
There was no attached. Do you have a link to an adapter ?
Rolling buckeye is offline   Reply With Quote
Old 04-27-2013, 06:57 PM   #12
Senior Member
 
fonzie's Avatar
 
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 4,167
I attached a file in post #7 and I can see it...you don't? Here it is again.....you need adobe acrobat reader to open
Attached Files
File Type: pdf Special Generator Pigtail Instructions.pdf (132.6 KB, 62 views)
__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2019 F350 Ruby Red 6.7l diesel 3.31 axle electronic locker
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2014 (18) 2015 (18) 2016 (36) 2017 (32) 2018 (42) 2019 (28) 2020 (35)
fonzie is offline   Reply With Quote
Old 04-27-2013, 06:59 PM   #13
Phat Phrog Stunt Team
 
Rolling buckeye's Avatar
 
Join Date: Feb 2013
Posts: 1,330
Quote:
Originally Posted by fonzie View Post
I attached a file in post #7 and I can see it...you don't? Here it is again.....you need adobe acrobat reader to open
Oh,I'm on an I pad,will check with desk top, Thanks again !
Rolling buckeye is offline   Reply With Quote
Old 04-28-2013, 06:16 AM   #14
Senior Member
 
fonzie's Avatar
 
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 4,167
Rolling, if you look at the attached boliy generator service manual, you will see that the ground and neutral are not connected together on the unit. That creates a floating neutral. Even if the generator is grounded to earth, there is still no referenced point for the PI and it shows and open ground. I just use the by-pass on my PI instead of the adapter. In a normal supply, the ground and neutral are tied together in the electrical panel and also grounded to mother earth. Hope this helps.
Attached Files
File Type: pdf boliy service manual.pdf (328.2 KB, 62 views)
__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2019 F350 Ruby Red 6.7l diesel 3.31 axle electronic locker
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2014 (18) 2015 (18) 2016 (36) 2017 (32) 2018 (42) 2019 (28) 2020 (35)
fonzie is offline   Reply With Quote
Old 04-28-2013, 07:01 AM   #15
Phat Phrog Stunt Team
 
Rolling buckeye's Avatar
 
Join Date: Feb 2013
Posts: 1,330
Quote:
Originally Posted by fonzie View Post
Rolling, if you look at the attached boliy generator service manual, you will see that the ground and neutral are not connected together on the unit. That creates a floating neutral. Even if the generator is grounded to earth, there is still no referenced point for the PI and it shows and open ground. I just use the by-pass on my PI instead of the adapter. In a normal supply, the ground and neutral are tied together in the electrical panel and also grounded to mother earth. Hope this helps.
Thanks fonzie ! Using the bypass worked,so I too will stick with that.
Rolling buckeye is offline   Reply With Quote
Old 04-28-2013, 09:55 AM   #16
Junior Member
 
raytronx's Avatar
 
Join Date: Apr 2013
Posts: 23
Nice little article explaining the problem and an easy solution.

Generator Ground-Neutral Bonding | No~Shock~Zone

Cheers Ray
__________________
Full-Time RVer, loving the life.

raytronx is offline   Reply With Quote
Old 04-28-2013, 03:15 PM   #17
Phat Phrog Stunt Team
 
Rolling buckeye's Avatar
 
Join Date: Feb 2013
Posts: 1,330
Quote:
Originally Posted by raytronx View Post
Nice little article explaining the problem and an easy solution.

Generator Ground-Neutral Bonding | No~Shock~Zone

Cheers Ray
Thank you Ray !
I think I can do THAT,probably with stuff around the garage.
Rolling buckeye is offline   Reply With Quote
Old 04-28-2013, 05:34 PM   #18
RV Electricity Expert
 
jmsokol's Avatar
 
Join Date: Apr 2013
Posts: 99
I'm Mike Sokol, the author of the No~Shock~Zone article about Ground-Neutral bonding (thanks for posting it, Ray).

I've confirmed that this neutral bonding jumper plug works with the engineering staff at Progressive Industries, as well as "off the record" with Honda technical support. And as noted previously on this thread, "grounding" your generator with a ground rod in the earth will do nothing to correct this problem, and it's not really a safety ground at all. Nope, all safety grounds must connect to the ground-neutral bonding point, which as I've indicated in the linked article above, DOES NOT EXIST on many (most?) small portable generators. My simple G-N bonding plug will only cost a buck or two and take 5 minutes to make. Just be sure to jump from the Green (Ground) screw to the White (Neutral) screw on the Edison plug. The Neutral blade is the "taller" one in an American outlet.

Please send this link to anybody you know using a portable generator to power their RV: Generator Ground-Neutral Bonding | No~Shock~Zone

Mike Sokol
mike@noshockzone.org
No Shock Zone
jmsokol is offline   Reply With Quote
Old 04-28-2013, 07:35 PM   #19
Phat Phrog Stunt Team
 
Rolling buckeye's Avatar
 
Join Date: Feb 2013
Posts: 1,330
Quote:
Originally Posted by jmsokol View Post
I'm Mike Sokol, the author of the No~Shock~Zone article about Ground-Neutral bonding (thanks for posting it, Ray).

I've confirmed that this neutral bonding jumper plug works with the engineering staff at Progressive Industries, as well as "off the record" with Honda technical support. And as noted previously on this thread, "grounding" your generator with a ground rod in the earth will do nothing to correct this problem, and it's not really a safety ground at all. Nope, all safety grounds must connect to the ground-neutral bonding point, which as I've indicated in the linked article above, DOES NOT EXIST on many (most?) small portable generators. My simple G-N bonding plug will only cost a buck or two and take 5 minutes to make. Just be sure to jump from the Green (Ground) screw to the White (Neutral) screw on the Edison plug. The Neutral blade is the "taller" one in an American outlet.

Please send this link to anybody you know using a portable generator to power their RV: Generator Ground-Neutral Bonding | No~Shock~Zone

Mike Sokol
mike@noshockzone.org
No Shock Zone
WOW ! Thanks !
I purchased the plug,today,and will wire jumper,and try it out tomorrow !
And yes, Thanks again Ray !
Rolling buckeye is offline   Reply With Quote
Old 04-28-2013, 08:11 PM   #20
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Mines not an inverter gennie and not small either.
I still learned something new today.

My gennie used to have a floating neutral 240/120 plug but has been changed to a standard rv 120/ 30 amp plug only.
TURBS is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 09:01 PM.