Quote:
Originally Posted by laurieann
Had to turn off the breaker and yes compressor ran with T stat off
|
The following chart shows the different electrical connections made by the thermostat during
operation. The chart below assumes12VDC(+) is supplied to thermostat Red wire R and that
12VDC(-) or ground is supplied to the Blue wire B at all times.
Thermostat Operations Internal 12VDC(+) Connections Made
Cool Mode Selected On Low Fan Red R to Yellow Y and Gray GL
Cool Mode Selected On High Fan Red R to Yellow Y and Green GH
Heat Mode Selected On Any Fan Speed
(Note: Furnace blower operates independently
from sequencer or time delay in furnace)
Red R to White W
Fan Only Selected (Hi-Fan Only) Red R to Green GH
Note: When the auto cool mode is selected on the thermostat the fan cycles on and off with the
compressor as needed. When the on cool mode has been selected the fan runs continuously and the
compressor cycles on and off as needed.
The following chart depicts thermostat wiring and the wiring destinations for air conditioners with
control boxes containing Printed Circuit Boards.
THERMOSTAT
TERMINAL /
WIRE
CONTROL AND SUPPLY
WIRING (OEM / VENDOR)
CEILING ASSEMBLY
TERMINAL
DESIGNATION
R or RED ONE RED, (+) 12VDC SUPPLY
WIRE TO THE THERMOSTAT
N /A
B or BLUE TWO BLUE, ONE (-) 12VDC SUPPLY WIRE
TO THE THERMOSTAT AND ONE BLUE
WIRE TO CEILING ASSEMBLY / PLENUM
B
Y or YELLOW ONE YELLOW, COMPRESSOR CONTROL
WIRE TO CEILING ASSEMBLY / PLENUM
Y
GH or GREEN ONE GREEN, HIGH FAN CONTROL WIRE
TO CEILING ASSEMBLY / PLENUM
GH
GL or GRAY ONE GRAY, LOW FAN CONTROL WIRE
TO CEILING ASSEMBLY / PLENUM
GL
W or WHITE ONE WHITE, 12VDC (+) FURNACE
CONTROL WIRE FROM THE
THERMOSTAT
FURNACE
NOTE: The (W) White wire is not available on COOL ONLY thermostats.
NOTE: THE CONNECTING WIRES TO THE THERMOSTAT ARE PROVIDED BY THE
The t Stat may be shorted or the wires behind the T stat may be shorted out. remove the t stat from the wall and reset the beaker. If it starts it may be the t stat. remove the yellow wire from t stat and see if A/C stops. If not problem may be the wires to the A/C or the A/C its self has a wiring problem.
Hope this helps Tim