Replacing Analog Thermostat on Dometic Furnace

flatland-FRF

New Member
Joined
Nov 29, 2024
Messages
2
I have a 2018 Coachmen Freelander 20CB with a Dometic propane furnace and the standard analog thermostat for the furnace only.


I purchased the Dometic Standard CT Single Zone digital thermostat to replace it.


When I pulled the old one I found it only has two wires to control the furnace but the digital thermostat has three connections. I tried connecting just two wires (pos and negtive) and the furnace starts, cycles, shuts off and then restarts right away. I get error code E1 as well (Loss of communication)


Can the new digital thermostat be configured for a two wire system? I can't find any diagrams for it and the thermostat only comes with user instructions, not wiring diagrams.

If this one will not work, is there a digital thermostat that will work with the two wire system?


Thanks,
Charlie
 
Last edited:
I just ordered that one yesterday, thanks.


With further research I found the third wire is listed as "Comms".


I'll return the Dometic CT and use the Honeywell.


I appreciate the response.
 