Greetings!
I’ve been asked a number of questions about the solar power installation and supporting modifications that we recently completed. (Yea, right…. Is any project ever really completed? I’m already looking at things to add to make it even better!) Anyway, I thought that I’d try to put together a single post that would explain our installation and answer any questions.
First, a little bit about us and why (we believe) solar was the right choice for us. We live in Upstate New York, in the Albany area. Our travel trailer is a 2009 Rockwood 2607, with a large front bedroom, mid-ship galley and living area, and a LARGE rear bathroom (the feature that “sold” us on the trailer)! While it’s a “2009”, it was delivered new in the winter of 2008, so it’s had three camping seasons. Each year, we go to a major RV show in Springfield, MA (plus several other smaller shows), and we have yet to see a RV whose floorplan appeals to us more than the one we already have, which tells us that we made the correct choice, and will likely keep this unit for years to come.
We typically camp in a variety of places, including some very nice RV resorts, private campgrounds, state parks with limited or no utilities, NASCAR races, and an occasional parking lot while in transit more than a day. One of our favorite trips is one that we try to repeat every other year, to Assateague IslandState Park, in Maryland. Camping at Assateague is truly boondocking. There are no services in all but one of the camping loops. Water needs to be hauled in, waste hauled out, and if power is needed, it means “disturbing the peace” by running a generator.
For boondocking, we have a 2400W Yamaha (quiet!) generator, purchased after our first NASCAR camping weekend without one, but using it means that someone needs to fuel it (me!), start it (also me!), keep an eye on it while it’s running (me again!), and then secure it when completed (yup, it’s me!). In spite of the Yamaha being quiet, this activity still requires “attention” – detracting from my camping leisure, burning long-dead dinosaurs whose remains directly fill the bank accounts of a society that includes those who would commit acts of terrorism (I’m a firefighter who worked on The Pile at Ground Zero in NYC post-9-11), and emiting CO and other toxins into my campsite!
So after a 2009 trip to Assateague, DW makes the suggestion that we look at solar. I blew it off as “too expensive” at the time, but started to look at exactly what “going solar” really meant. In July 2010 we, once again, managed to book our sites at Assateague for 10-days in July 2011, so I knew then that I had a year to move on this.
In the Spring of 2010 (after two seasons of use), the original Group 24 marine deep-cycle battery was toast. My solar research and rough consumption calculations had already told me that I needed to get more than 200Ah of capacity, and that I was best-off doing this with a pair of 6-volt golf-cart batteries, which I purchased from Sam’s Club, giving me 220Ah.
By the fall of 2010 I had really gotten into the research. I knew that the first two solar “systems” that I had looked at would never fill my needs. These were the 45W system sold by Harbor Freight, and the Northern Tool 60W system. Both would support most of my daytime use (primary daytime user is the water pump), and would take care of most of the parasite loads (smoke detector, LP detector, refrigerator circuit board), but would never be capable of bringing the batteries back to full charge. This would mean that I’d still need to run the generator every day or two to restore the batteries anyway. So towards the end of the 2010 season, I started asking questions, reading manufacturer’s information, taking measurements, and re-designing my electrical system to integrate solar power.
There are three major subgroups of work involved in my project. These are reducing load, distributing 12v availability inside the living area, and installing the roof-mounted solar collection system.
Reducing Load
For me, the single area where I could most reduce load was with interior and exterior convenience lighting. The unit came from the factory with at least seventeen 921-type incandescent bulbs, and a couple of other individual style of bulbs in various fixtures. I counted what I’d need to replace these with LED’s, and I ordered LED replacements. I found an on-line (Chinese) supplier, ordered one each of what I needed to assure that it was what I really wanted to do, and after trying them out, ordered what I needed. I even replaced the incandescent bulbs in the range hood and the refrigerator. All LEDs were ordered from Virtual Village.com .
Distributing 12V Availability Inside the Living Area
I carry a cell phone (personal) and a PDA (work); plus my wife has a PDA. All three have cigarette-lighter chargers. We both have cameras that can recharge directly from 12v, plus spare battery chargers for the cameras that also can recharge this way. I have a 12v cigarette plug charger for my laptop. In the past, we had to put these devices in the tow vehicle to charge. This made them unavailable for use, and was inconvenient. So I added five 12v cigarette lighter plug outlets in various locations; one on each side of the bed, one on the exposed wood side of the couch, one on the wall over the kitchen counter, and one on the kick-panel (behind your legs) on a dinette bench. The outlets were Prime Products 08-5010 12 V Standard Plate Receptacle, ordered from Amazon.com .
To wire this, I cut into the primary 12v supply and ground in the pass-through nose compartment, about 3 feet away from the batteries. From this location, I ran a pair of #10 wires about 5 feet to a location inside the pass-through, but easily reachable from the outside. The positive lead is protected at this location with a 30A in-line fuse, which then feeds a 4-fuse fuseblock (purchased at a local automotive supply store). Each fuse then feeds a single circuit (run with #12 wire) and outlet, with one circuit having two outlets to feed. Each of these circuits has an individual 15A fuse.
Roof Mounted Solar Collection
Anyone who has read this far, is likely looking to get to this section. Our solar system is comprised of the following:
Two 150W Suntech Panels (34.4v) – These came from Sun Electric, in Phoenix., as did the wire pigtails necessary to go from the panel to the combiner box. I used pigtails joined to the factory panel connector, as some folks report that cutting the factory connection off and wiring with a crimp connector voids factory panel warranties.
Homemade two axis, four way tilting mounts – Assorted aluminum stock, clevis pins and stainless steel nuts, bolts, and screws came from local Home Depot, Lowes, and True Value Hardware. The stainless steel hinges came from HardwareSource.com . The design attaches (with removable pivot-pins) the panels to the roof of the unit in six points for travel or to use flat. The pivots, one in each corner, allow for the panel to be lifted on either end of the long axis. The hinges, three on each side, allow the panels to be lifted on either side of the short axis. Prop-rods of various lengths, with pin holes drilled every inch, allow for angle adjustment of the panel to accommodate different latitudes, seasons, and whether the unit is oriented N/S or E/W. For example, at my house (near Albany, NY @ latitude 42.6710), in the Spring or Fall I need a 39.5 degree angle. If parked N/S, the panels will be lifted from the North end a height of 43”. If parked E/W, the angle stays the same but the lift to achieve it is 21.5” (so I round up or down for early or late season). It the summer the two lifts are 17” and 8.5”, respectively.
Panel Disconnect – Installed to disconnect power from panels to controller for maintenance, storage, etc. Purchased on-line from Amazon.com is a Perko Marine Battery Switch, Model 9601DP.
Rogue MTP-3024 Controller/Charger – This is the new 3024! In fact, my invoice was 2011-1, which Rogue’s owner, Mark Loring, confirmed was the first of the new 3024’s shipped. I can’t say enough good about working with Marc and Rogue. He answered several questions for me with detailed answers prior to my order, and while discussing via email the progress of my install prior to him being ready to ship the new models, he readily shipped the battery temp sensor and wire so that I could pre-wire.
Roof Combiner Box and Interior Junction Box – These are a matching pair of 4/2 Roof C-Box from AMSolar. Good boxes to work with, with large access points on buss-bars. They mount and seal well, too.
150W catastrophic fuse - Raptor RANL1502 150 Amp ANL Fuses, 24K Gold Plated, 2 Pack and a Scosche EWFH Single ANL Fuse Holder, both from Amazon.com .
#4 Cable - F29740320-A RADAFLEX® #4 AWG Twin Cable from CableYard.com
I also needed to purchase a hydraulic crimping tool to make-up the cables and attach lugs for various junctions. The lugs came from local auto supply stores, but the hydraulic crimp came from Harbor Freight.
System costs – rounded off (what you’ve been hanging on for) are as follows. All costs include shipping, where applicable:
Solar Panels: $756
Pigtail: $26
Controller: $370
Stainless Steel Hinges: $50
Aluminum Stock: $120
Nuts, Bolts, Screws, Pins:$30
Panel Disconnect: $38
Combiner Boxes: $149
Catastrophic Fuse Holder & Fuses: $25
#4 Cable: $79
6-volt batteries: $165
In-line fuse holder: $4
4-fuse block: $7
12v Receptacle Plates: $29
Battery lug crimps: $15
Hydraulic crimping tool: $50
Two tubes of Dicor Roof Sealant: $22
#10 & #12 wire, wire crimps, heat-shrink tubing, clamps, etc: $50
TOTAL SYSTEM COST: $1,985 of this, $425+ is in shipping and handling!
A number of photos showing much of the install can be viewed at: Rockwood Solar Install 2011 pictures by Fire_Instructor - Photobucket
So how does it all work??? It’s all been operational since last Saturday afternoon (June 18, 2011). It brought the battery up to full that day, and has held it there ever since. That said, up until today (June 22), we’ve had sun-filled days, and the trailer has been parked in my driveway. Only parasite loads and short-duration “other” loads (lights, sat radio, water pump) have occurred. Today was rainy and very overcast. The contoller went into sleep mode twice during the day because of lack of panel output in the stormy, overcast sky, yet the times that it was awake, it still maintained a “full” battery, and operated in the float mode. Our Assateague trip starts a week from today, so I’ll know just how good the entire system is in just a few short weeks.
So that about wraps it up. About the only thing left that I haven’t told you is blood-type: (B neg).
My apologies for being so long, but I warned you!!!! I hope that you got something from the read, and hopefully this answered any questions, and gave you some solar meat to chew on for a while…..
Be Safe,
Rick
Fire Instructor
Greetings!
I’ve been asked a number of questions about the solar power installation and supporting modifications that we recently completed. (Yea, right…. Is any project ever really completed? I’m already looking at things to add to make it even better!) Anyway, I thought that I’d try to put together a single post that would explain our installation and answer any questions.
First, a little bit about us and why (we believe) solar was the right choice for us. We live in Upstate New York, in the Albany area. Our travel trailer is a 2009 Rockwood 2607, with a large front bedroom, mid-ship galley and living area, and a LARGE rear bathroom (the feature that “sold” us on the trailer)! While it’s a “2009”, it was delivered new in the winter of 2008, so it’s had three camping seasons. Each year, we go to a major RV show in Springfield, MA (plus several other smaller shows), and we have yet to see a RV whose floorplan appeals to us more than the one we already have, which tells us that we made the correct choice, and will likely keep this unit for years to come.
We typically camp in a variety of places, including some very nice RV resorts, private campgrounds, state parks with limited or no utilities, NASCAR races, and an occasional parking lot while in transit more than a day. One of our favorite trips is one that we try to repeat every other year, to Assateague IslandState Park, in Maryland. Camping at Assateague is truly boondocking. There are no services in all but one of the camping loops. Water needs to be hauled in, waste hauled out, and if power is needed, it means “disturbing the peace” by running a generator.
For boondocking, we have a 2400W Yamaha (quiet!) generator, purchased after our first NASCAR camping weekend without one, but using it means that someone needs to fuel it (me!), start it (also me!), keep an eye on it while it’s running (me again!), and then secure it when completed (yup, it’s me!). In spite of the Yamaha being quiet, this activity still requires “attention” – detracting from my camping leisure, burning long-dead dinosaurs whose remains directly fill the bank accounts of a society that includes those who would commit acts of terrorism (I’m a firefighter who worked on The Pile at Ground Zero in NYC post-9-11), and emiting CO and other toxins into my campsite!
So after a 2009 trip to Assateague, DW makes the suggestion that we look at solar. I blew it off as “too expensive” at the time, but started to look at exactly what “going solar” really meant. In July 2010 we, once again, managed to book our sites at Assateague for 10-days in July 2011, so I knew then that I had a year to move on this.
In the Spring of 2010 (after two seasons of use), the original Group 24 marine deep-cycle battery was toast. My solar research and rough consumption calculations had already told me that I needed to get more than 200Ah of capacity, and that I was best-off doing this with a pair of 6-volt golf-cart batteries, which I purchased from Sam’s Club, giving me 220Ah.
By the fall of 2010 I had really gotten into the research. I knew that the first two solar “systems” that I had looked at would never fill my needs. These were the 45W system sold by Harbor Freight, and the Northern Tool 60W system. Both would support most of my daytime use (primary daytime user is the water pump), and would take care of most of the parasite loads (smoke detector, LP detector, refrigerator circuit board), but would never be capable of bringing the batteries back to full charge. This would mean that I’d still need to run the generator every day or two to restore the batteries anyway. So towards the end of the 2010 season, I started asking questions, reading manufacturer’s information, taking measurements, and re-designing my electrical system to integrate solar power.
There are three major subgroups of work involved in my project. These are reducing load, distributing 12v availability inside the living area, and installing the roof-mounted solar collection system.
Reducing Load
For me, the single area where I could most reduce load was with interior and exterior convenience lighting. The unit came from the factory with at least seventeen 921-type incandescent bulbs, and a couple of other individual style of bulbs in various fixtures. I counted what I’d need to replace these with LED’s, and I ordered LED replacements. I found an on-line (Chinese) supplier, ordered one each of what I needed to assure that it was what I really wanted to do, and after trying them out, ordered what I needed. I even replaced the incandescent bulbs in the range hood and the refrigerator. All LEDs were ordered from Virtual Village.com .
Distributing 12V Availability Inside the Living Area
I carry a cell phone (personal) and a PDA (work); plus my wife has a PDA. All three have cigarette-lighter chargers. We both have cameras that can recharge directly from 12v, plus spare battery chargers for the cameras that also can recharge this way. I have a 12v cigarette plug charger for my laptop. In the past, we had to put these devices in the tow vehicle to charge. This made them unavailable for use, and was inconvenient. So I added five 12v cigarette lighter plug outlets in various locations; one on each side of the bed, one on the exposed wood side of the couch, one on the wall over the kitchen counter, and one on the kick-panel (behind your legs) on a dinette bench. The outlets were Prime Products 08-5010 12 V Standard Plate Receptacle, ordered from Amazon.com .
To wire this, I cut into the primary 12v supply and ground in the pass-through nose compartment, about 3 feet away from the batteries. From this location, I ran a pair of #10 wires about 5 feet to a location inside the pass-through, but easily reachable from the outside. The positive lead is protected at this location with a 30A in-line fuse, which then feeds a 4-fuse fuseblock (purchased at a local automotive supply store). Each fuse then feeds a single circuit (run with #12 wire) and outlet, with one circuit having two outlets to feed. Each of these circuits has an individual 15A fuse.
Roof Mounted Solar Collection
Anyone who has read this far, is likely looking to get to this section. Our solar system is comprised of the following:
Two 150W Suntech Panels (34.4v) – These came from Sun Electric, in Phoenix., as did the wire pigtails necessary to go from the panel to the combiner box. I used pigtails joined to the factory panel connector, as some folks report that cutting the factory connection off and wiring with a crimp connector voids factory panel warranties.
Homemade two axis, four way tilting mounts – Assorted aluminum stock, clevis pins and stainless steel nuts, bolts, and screws came from local Home Depot, Lowes, and True Value Hardware. The stainless steel hinges came from HardwareSource.com . The design attaches (with removable pivot-pins) the panels to the roof of the unit in six points for travel or to use flat. The pivots, one in each corner, allow for the panel to be lifted on either end of the long axis. The hinges, three on each side, allow the panels to be lifted on either side of the short axis. Prop-rods of various lengths, with pin holes drilled every inch, allow for angle adjustment of the panel to accommodate different latitudes, seasons, and whether the unit is oriented N/S or E/W. For example, at my house (near Albany, NY @ latitude 42.6710), in the Spring or Fall I need a 39.5 degree angle. If parked N/S, the panels will be lifted from the North end a height of 43”. If parked E/W, the angle stays the same but the lift to achieve it is 21.5” (so I round up or down for early or late season). It the summer the two lifts are 17” and 8.5”, respectively.
Panel Disconnect – Installed to disconnect power from panels to controller for maintenance, storage, etc. Purchased on-line from Amazon.com is a Perko Marine Battery Switch, Model 9601DP.
Rogue MTP-3024 Controller/Charger – This is the new 3024! In fact, my invoice was 2011-1, which Rogue’s owner, Mark Loring, confirmed was the first of the new 3024’s shipped. I can’t say enough good about working with Marc and Rogue. He answered several questions for me with detailed answers prior to my order, and while discussing via email the progress of my install prior to him being ready to ship the new models, he readily shipped the battery temp sensor and wire so that I could pre-wire.
Roof Combiner Box and Interior Junction Box – These are a matching pair of 4/2 Roof C-Box from AMSolar. Good boxes to work with, with large access points on buss-bars. They mount and seal well, too.
150W catastrophic fuse - Raptor RANL1502 150 Amp ANL Fuses, 24K Gold Plated, 2 Pack and a Scosche EWFH Single ANL Fuse Holder, both from Amazon.com .
#4 Cable - F29740320-A RADAFLEX® #4 AWG Twin Cable from CableYard.com
I also needed to purchase a hydraulic crimping tool to make-up the cables and attach lugs for various junctions. The lugs came from local auto supply stores, but the hydraulic crimp came from Harbor Freight.
System costs – rounded off (what you’ve been hanging on for) are as follows. All costs include shipping, where applicable:
Solar Panels: $756
Pigtail: $26
Controller: $370
Stainless Steel Hinges: $50
Aluminum Stock: $120
Nuts, Bolts, Screws, Pins:$30
Panel Disconnect: $38
Combiner Boxes: $149
Catastrophic Fuse Holder & Fuses: $25
#4 Cable: $79
6-volt batteries: $165
In-line fuse holder: $4
4-fuse block: $7
12v Receptacle Plates: $29
Battery lug crimps: $15
Hydraulic crimping tool: $50
Two tubes of Dicor Roof Sealant: $22
#10 & #12 wire, wire crimps, heat-shrink tubing, clamps, etc: $50
TOTAL SYSTEM COST: $1,985 of this, $425+ is in shipping and handling!
A number of photos showing much of the install can be viewed at: Rockwood Solar Install 2011 pictures by Fire_Instructor - Photobucket
So how does it all work??? It’s all been operational since last Saturday afternoon (June 18, 2011). It brought the battery up to full that day, and has held it there ever since. That said, up until today (June 22), we’ve had sun-filled days, and the trailer has been parked in my driveway. Only parasite loads and short-duration “other” loads (lights, sat radio, water pump) have occurred. Today was rainy and very overcast. The contoller went into sleep mode twice during the day because of lack of panel output in the stormy, overcast sky, yet the times that it was awake, it still maintained a “full” battery, and operated in the float mode. Our Assateague trip starts a week from today, so I’ll know just how good the entire system is in just a few short weeks.
So that about wraps it up. About the only thing left that I haven’t told you is blood-type: (B neg).
My apologies for being so long, but I warned you!!!! I hope that you got something from the read, and hopefully this answered any questions, and gave you some solar meat to chew on for a while…..
Be Safe,
Rick